Make the most of your remote operations with end-to-end solutions with Process Automation’s SCADA and Telemetry Solutions. With the challenges that remote sites present, reliable communications for remote operation, monitoring & management are vital in enhancing productivity and ensuring profitability.
cancel
Showing results for 
Show  only  | Search instead for 
Did you mean: 
Cadet

Changing Button Symbol Appearance Based On Current Mimic Name

I am trying to change the properties of a button symbol based on the mimc that is open. For example, I have 5 menu buttons that open/navigate to other mimics via pick action hyperlink, but I want Button 1 to be yellow or disappear (in the code below) since the mimic that opens, is the one that is currently open. I'm not real handy with VB/Scripting.

 

I have the following in the Mimic Script

 

sub Mimic_Load()
   call ButtonMod()
end sub

 

sub ButtonMod()
   if Mimic.FullName = "SA.Sites.Overview.Communication Statistics Overview L1" then
      btn_Booster1.Visible = False
   else
      btn_Booster1.Visible = True
   end if
end sub

 

 

I know that the fullname property is correct as I've done a MsgBox and returned that name and the error happens at the success point where btn_Booster1.Visible happens. The error I get is "Object required: 'btn_Booster1'". And yes, there is a button symbol on the Mimic and its name is btn_Booster1.

 

5 REPLIES 5
Highlighted
Ensign

Re: Changing Button Symbol Appearance Based On Current Mimic Name

I would just use the Animations for Color and Visible and not a script.

 

But to answer your question you want 

 

btn_Booster1.Visible, False

Highlighted
Lieutenant JG

Re: Changing Button Symbol Appearance Based On Current Mimic Name

As @geoffpatton recommends, use the Visible animation for this.

On the animations dialog...

 

It's where other people will expect such animations to be located.

 

 

As for your actual script, I've got a terrible memory for these things and the exact syntax.  But I believe you may have to specify the full path to the object, ie. with the appropriate layer also.

I thought there was an example for this in the help, but maybe it was in the Schneider training material.

 

I found it 🙂

 

file:///C:/ProgramData/Schneider%20Electric/ClearSCADA/Help_en-US/Content/ScriptingGuide/Mimic.Layers.htm%3FTocPath%3DCore%2520Reference%7CCoding%7CScripting%7CMimic%2520Functions%2520and%2520Properties%7CMimic%2520Properties%7CMimic.Layers%7C_____0

 

hmm... it seems copying the shortcut, or trying to Open in new Window with GeoSCADA help doesn't work...

You want the scripting section, and then Mimic Properties, and then Mimic.Layers

Core Reference > Coding > Scripting > Mimic.Layers

 

So you should be doing

Mimic.Layers("{NAME OF LAYER HERE}").Item("{NAME OF ITEM HERE"}).Visible = False

 

I just tested it.. and now I've lost a good button...


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Highlighted
Ensign

Re: Changing Button Symbol Appearance Based On Current Mimic Name

Oh duh, I was thinking of writing to a database object.

 

Something like this

 

Mimic.Layers("Graphical").Item("ForcePoll").Visible = True

Highlighted
Cadet

Re: Changing Button Symbol Appearance Based On Current Mimic Name

Thanks! That worked wonderfully!

Highlighted
Cadet

Re: Changing Button Symbol Appearance Based On Current Mimic Name

Thanks! That worked wonderfully!