Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
65 | |
46 | |
28 | |
27 |
Link copied. Please paste this link to share this article on your social media post.
Hello Everyone, i have a question about de configuration SMTP in COMX 510.
Actually I'm using a com X conected to a router 3G. That router is with a BAM from a mobile company.
When i want to public data, appear this msge:
I configure the COMX like this:
Exist any problem for publish in CSV with SMTP configuration using internet 3G from a mobile company??
Thanks for all.
Link copied. Please paste this link to share this article on your social media post.
Hi,
Some cellular providers will block SMTP traffic (especially over port 25). Please confirm that this traffic is allowed with BAM customer service.
Best,
Colton
Link copied. Please paste this link to share this article on your social media post.
Hi Colton:
I prove the same configuration with Another Com X, and it works with the same BAM.
I dont know if the problem would be the traffic in the BAM :/.
When i try to publish with the other COMX, appear this message: " Check the registers for details".
Any idea?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hi Camilo,
Can you share a screenshot of the message you see and the diagnostic file (Found in Maintenance -> Logs -> Get Diagnostics)?
Best,
Colton
Link copied. Please paste this link to share this article on your social media post.
Colton:
I Could solve the problem. I had to configure correctly the Gateway and DSN with the information of the BAN. Now I Can sent information thought e-mail using a BAM internet.
Regards!
Thanks for all!
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.