Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80861members
346945posts

Modbus data collection by PAS600 Panel server through Link 150 gateway

Solved
Gingko_Elec
Lieutenant JG
Lieutenant JG
0 Likes
3
435

Modbus data collection by PAS600 Panel server through Link 150 gateway

Can you please confirm if PAS600 Panel server can collect data into Modbus serial line devices through a Link 150 gateway ?

 

Best

GE​

Tags (1)

Accepted Solutions
Romain_Polette
Sisko Sisko
Sisko
0 Likes
1
424

Re: Modbus data collection by PAS600 Panel server through Link 150 gateway

Hello @Gingko_Elec , 

 

This will be possible soon.

Just waiting the developers to deliver the version 001.003.001.

 

@Dom-Socquet Do you have visibility when the next PAS600 release will be available on se.com ?

 

Thanks.

Romain POLETTE - Global Expert Technical Support - Digital Power Division
38EQI - Eybens - France

See Answer In Context

Tags (1)
3 Replies 3
Thierry_Baudard
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
425

Re: Modbus data collection by PAS600 Panel server through Link 150 gateway

Hello Gingko Elec,

 

Yes, it is possible.

In this architecture, the Link 150 will be designed as a “child gateway” for the Panel Server.

For this architecture, PAS600 firmware must be Version 001.003.001  or higher.

Thierry BAUDARD
Digital Power Technical Pre sale support International Hub
Tags (1)
Romain_Polette
Sisko Sisko
Sisko
0 Likes
1
425

Re: Modbus data collection by PAS600 Panel server through Link 150 gateway

Hello @Gingko_Elec , 

 

This will be possible soon.

Just waiting the developers to deliver the version 001.003.001.

 

@Dom-Socquet Do you have visibility when the next PAS600 release will be available on se.com ?

 

Thanks.

Romain POLETTE - Global Expert Technical Support - Digital Power Division
38EQI - Eybens - France
Tags (1)
Szymon_Hochół
Commander Commander
Commander
0 Likes
0
372

Re: Modbus data collection by PAS600 Panel server through Link 150 gateway

The v1.3.1 firmware for PAS600 is already available on se.com.

 

Best regards

Tags (1)