Modbus data collection by PAS600 Panel server through Link 150 gateway

Solved
Gingko_Elec
Lieutenant JG
Lieutenant JG
0 Likes
3
434

Modbus data collection by PAS600 Panel server through Link 150 gateway

Can you please confirm if PAS600 Panel server can collect data into Modbus serial line devices through a Link 150 gateway ?

 

Best

GE​

Tags (1)

Accepted Solutions
Romain_Polette
Sisko Sisko
Sisko
0 Likes
1
423

Re: Modbus data collection by PAS600 Panel server through Link 150 gateway

Hello @Gingko_Elec , 

 

This will be possible soon.

Just waiting the developers to deliver the version 001.003.001.

 

@Dom-Socquet Do you have visibility when the next PAS600 release will be available on se.com ?

 

Thanks.

Romain POLETTE - Global Expert Technical Support - Digital Power Division
38EQI - Eybens - France

See Answer In Context

Tags (1)
3 Replies 3
Thierry_Baudard
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
424

Re: Modbus data collection by PAS600 Panel server through Link 150 gateway

Hello Gingko Elec,

 

Yes, it is possible.

In this architecture, the Link 150 will be designed as a “child gateway” for the Panel Server.

For this architecture, PAS600 firmware must be Version 001.003.001  or higher.

Thierry BAUDARD
Digital Power Technical Pre sale support International Hub
Tags (1)
Romain_Polette
Sisko Sisko
Sisko
0 Likes
1
424

Re: Modbus data collection by PAS600 Panel server through Link 150 gateway

Hello @Gingko_Elec , 

 

This will be possible soon.

Just waiting the developers to deliver the version 001.003.001.

 

@Dom-Socquet Do you have visibility when the next PAS600 release will be available on se.com ?

 

Thanks.

Romain POLETTE - Global Expert Technical Support - Digital Power Division
38EQI - Eybens - France
Tags (1)
Szymon_Hochół
Commander Commander
Commander
0 Likes
0
371

Re: Modbus data collection by PAS600 Panel server through Link 150 gateway

The v1.3.1 firmware for PAS600 is already available on se.com.

 

Best regards

Tags (1)