Dear All,
How can I connect and setup for communication setting on EGX300 into CM3000?
Once I have tested before, I used 2 wire cable to connect serially from EGX300 to CM3000, set ID address, baud rate and also parity on CM3000 with same on EX300 , then I run feature "Discover". But, EGX300 cannot detect anything.
I hope all you guys can share the information here.
Thank you.
Link copied. Please paste this link to share this article on your social media post.
EGX300 User Manual is the first step.
If you are sure about wiring, then another way to check if your CM3000 is properly connected, is by reading its registers:
- either from Diagnostics page > Read Device Registers
- or with a ModbusTCP Client software (ModScan, Mobus Poll, PMCModbus, etc...) from EGX300's IP and CM3000 SlaveID
If you can't read (timeouts) it worth checking:
- EGX300 Settings > Serial Port > Transmission Mode: Automatic, Response Timeout ...
- wiring
- terminators if any
- dip switch settings on EGX300
Send a screenshot of the EGX300 Diagnostics > Statistics page to Technical Support along with more information about your existing settings.
Link copied. Please paste this link to share this article on your social media post.
EGX300 User Manual is the first step.
If you are sure about wiring, then another way to check if your CM3000 is properly connected, is by reading its registers:
- either from Diagnostics page > Read Device Registers
- or with a ModbusTCP Client software (ModScan, Mobus Poll, PMCModbus, etc...) from EGX300's IP and CM3000 SlaveID
If you can't read (timeouts) it worth checking:
- EGX300 Settings > Serial Port > Transmission Mode: Automatic, Response Timeout ...
- wiring
- terminators if any
- dip switch settings on EGX300