Hello,
I have noticed that Com'X can not visualise negative"Active Power", hystorical trending freezes when you want to visualise:
That's a pity, you can not use a com'x when you have both received and delivered energy or negative and positive power
Is this a known issue?
Kind Regards
Koen
Link copied. Please paste this link to share this article on your social media post.
Hi Koen,
Sorry to hear you're running into trouble, what version of the ComX510 are you using?
Best,
Colton Peltier
Link copied. Please paste this link to share this article on your social media post.
Hello Colton,
Firmware:
Tomorrow I will test this with the latest firmware in our lab.
Kind regards
Koen
Link copied. Please paste this link to share this article on your social media post.
Colton,
Did the test with firmware version
Here the same problem, no negative power...
Kind Regards
Koen
Link copied. Please paste this link to share this article on your social media post.
Hi Koen,
I'm sorry you're experiencing this issue. I also tested on 3.5.15, and was able to recreate the exact issue you specified. When I tried our newest development snapshot of the firmware, I was not able to recreate the issue. I spoke with the engineering team, and they confirmed that this issue had been discovered and corrected recently. The fix for this issue will be included in our next release (Q2 this year). Here is a image of the corrected dashboard:
Best Regards,
Colton Peltier
Link copied. Please paste this link to share this article on your social media post.
Hello,
any news on this problem? because I have similar case on customer comx510
as you can see here: ComX510 does not show negative values at trend visualization
Link copied. Please paste this link to share this article on your social media post.
Latest firmware version for the energy server COM'X 510 (Version 3.6.3)