Bringing in data with Automation Server into Com'X510
Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2019-02-2005:35 AM
You can set the Automation Server as a ModBus Server. Create an interface ModBus TCP Server and under them add the values you want (and link these values to the "real" points). Then you go to the COm'X and add the AS as a TCP Device and map the point you've created.