Hi Everyone
I installed a COM'X510 with 9 Power Meters. 4 of them are PM5330 and 5 of them are PM820MG. All of them are conected by a MODBUS, but i have a problem.
The COM'X detect all ID's, but only recognize the PM5330, the PM820MG doesn't recognize it.
What can I do?
Can be a problem with Firmware of the PM820?
Thanks for all!!
Regards!
Link copied. Please paste this link to share this article on your social media post.
Can start with confirming that the PM800s have the same serial settnigs (8E1 vs 8O1 vs 8N1) as other devices and that the baud rates match the gateway.
Link copied. Please paste this link to share this article on your social media post.
All are in Modbus RTU, 19200 Bdu, non parity.
Link copied. Please paste this link to share this article on your social media post.
Hi man, i can fix it. I must configure the Com X with "1" in the end bit!!
Thanks for all!
Link copied. Please paste this link to share this article on your social media post.
Glad to hear you got it working!