Hi Guys,
Anyone knows the differences between these two relays:
CKIT-VMD1B-F24A
FKIT-VMD1B-C24A
The CKIT is no longer available and I can't find the differences.
BR,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-03 05:59 PM . Last Modified: 2021-08-03 06:01 PM
Hello,
Question:
Anyone knows the differences between these two relays:
CKIT-VMD1B-F24A
FKIT-VMD1B-C24A
The CKIT is no longer available and I can't find the differences.
Answer:
The "CKIT-" and "FKIT-" refer to the socket (base).
They are kits with a relay "and" a socket (shipped separated) .
CKIT- is the standard base, open (not covered) terminal screws
FKIT- is the full feature base, closed terminal (covered) terminal screws.
The VMD1B-F24A is the relay (F= full feature, 24A = 24VAC coil with push button and lever)
The VMD1C-C24A is the relay (C= standard, 24A = 24VAC coil)
The kits have been confusing and many of them have been eliminated.
Some of the "C" bases have been eliminated also due to lack of demand.
Many relays and sockets continue to be available as individual items but not in kits..
See the Veris website/catalog under Socket Relays for further details.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-03 05:59 PM . Last Modified: 2021-08-03 06:01 PM
Hello,
Question:
Anyone knows the differences between these two relays:
CKIT-VMD1B-F24A
FKIT-VMD1B-C24A
The CKIT is no longer available and I can't find the differences.
Answer:
The "CKIT-" and "FKIT-" refer to the socket (base).
They are kits with a relay "and" a socket (shipped separated) .
CKIT- is the standard base, open (not covered) terminal screws
FKIT- is the full feature base, closed terminal (covered) terminal screws.
The VMD1B-F24A is the relay (F= full feature, 24A = 24VAC coil with push button and lever)
The VMD1C-C24A is the relay (C= standard, 24A = 24VAC coil)
The kits have been confusing and many of them have been eliminated.
Some of the "C" bases have been eliminated also due to lack of demand.
Many relays and sockets continue to be available as individual items but not in kits..
See the Veris website/catalog under Socket Relays for further details.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.