Hello,
Could you please support if TC903 can control controlling Cooling valve (0-10v) and Electrical Heater (Digital)?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-21 03:16 AM . Last Modified: 2022-10-19 01:09 AM
Hi @Harris69
The TC900 appear to be either both proportional (0-10v outputs) or both outputs 2 position on/off.
An I/O module (0-10v in - digital output) with adjustable switching point could be used with the TC900 proportional version. An example here from a 3rd party supplier:
https://www.sontay.com/en-gb/products/io-input-output-modules/io-rm-relay-modules/
Or a high impedance relay could be used, the following KB indicates 250ohm minimum impedance, but may be best to aim for a coil impedance higher than this, note the pull in point may vary:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-21 03:16 AM . Last Modified: 2022-10-19 01:09 AM
Hi @Harris69
The TC900 appear to be either both proportional (0-10v outputs) or both outputs 2 position on/off.
An I/O module (0-10v in - digital output) with adjustable switching point could be used with the TC900 proportional version. An example here from a 3rd party supplier:
https://www.sontay.com/en-gb/products/io-input-output-modules/io-rm-relay-modules/
Or a high impedance relay could be used, the following KB indicates 250ohm minimum impedance, but may be best to aim for a coil impedance higher than this, note the pull in point may vary:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-25 12:38 AM
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.