Posted: 2021-05-26 01:59 PM
We have been requested to monitor only approximately 30 hospital rooms for T/H and I would like to be able to daisy chain these back to the AS-P as an integration. I will also need to confirm the quantity we can support on one comm bus back to the AS-P.
Is there a Temp/Humidity Sensor that we can use with EBO that communicates via BACnet mstp or Modbus RTU? I have looked at the SE8000's and the SmartX sensors (Ethernet sensor Bus) but they are not ideal for the reasons below.
The SmartX Living Sensors could be an option but the quantity you can put on a daisy chain is up to 4 and limited to a 200' distance. Also I would need to include multiple MP or RP field controllers to support the sensor bus under the AS-P. That adds a good amount of cost.
The SE8000's could be an option but I really only need the T/H monitoring so if there's something without all the I/O that would be preferred.
Any insight on another device would be very much appriciated,
Thanks,
Nicole Gonzalez
Acct Exec
Chicago Buildings Branch
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-27 04:54 AM
I'm unfamiliar with these (or atleast I believe I am). A google search came up with no results. Can you share a link to these or a model # I can better identify these from?
Thank you,
Nicole
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-27 05:06 AM
Hi,
SpaceLogic SLP Series Humidity Sensors (temperature included) https://ecoxpert.se.com/search?documentUUID=10d66b41-5e87-49fc-9084-83f04e647fa7&title=SpaceLogic%20...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-27 05:20 AM
Think you should be able to find some info about them if you search for "SLPSTX2" on Exchange or maybe on the Internet.
Please note that I have not used them myself,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-27 05:33 AM
Thank you, I was unaware these existed and look like a viable solution!
Very much appriciated,
Nicole
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-20 04:44 PM
I know this is late, but perhaps it will help someone else. These work well, and are easy to integrate: CW2XP2A Veris CW2 Protocol Series Air Quality Sensor, CO2, Wall, Replaceable Humidity 2%, Temperature Transmitter, BACnet MSTP/Modbus. They are available through iportal.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-21 09:46 AM
Have you looked at the SpaceLogic SLP sensors:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-23 07:39 AM
@DavidChild wor, nice! Thank you for adding these into the conversation!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-30 04:06 AM
Do you have Smart Widget files to Modbus and BACnet devices?
Link copied. Please paste this link to share this article on your social media post.