Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • Industrial Automation
  • :
  • Fabrika ve Makina Otomasyonu Çözümleri
  • :
  • Re: M218 controller back-up alma problemi
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49318members
Join Now
242550posts
Join Now

M218 controller back-up alma problemi

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Fabrika ve Makina Otomasyonu Çözümleri
Solved
esra
Crewman esra
Crewman
‎2020-06-18 02:49 AM
1 Like
3
797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-18 02:49 AM

M218 controller back-up alma problemi

Merhabalar;

 

Esas problemim; TM218 lerden nasıl backup alacağım.

 

Sorun ile ilgili bu zamana kadar toplamış olduğum bilgiler ise;

Sahamızda bulunan M218 CPU lardan (TM218LDA40DR2HN ve TM218LDA16DRN) back-up almak istiyorum.

Windows10 sanal bilgisayarıma, müsteri destek hattını arayarak temiz ettiğim “SoMachine V4.3” programını kurup, “local kod” ile M218 controllerı aktif ettim. miniUSB-USB kabloyu kullanarak PLC yi PC ye bağladım.

  1. “Device manager"dan bağlantımı kontrol ettiğimde kabloyu görüyorum.

    1_device_manager.JPG

     

     

  2. SoMachine V4.3 programını açıp, “maintenance” menüsünden “controller assistant” dan PLC yi görebiliyorum.

    2_maintenance_controllerassistant.JPG

     

    3_maintenance_controllerassistant_manageimages.JPG

     

    4_maintenance_controllerassistant_readfrom.JPG

      

  3. Burada “connect” dediğim zaman aşağıdaki hata ile karşılaşıyorum.

     5_maintenance_controllerassistant_connect.JPG

     

  4. PLC den Upload için “conncet controller” a geldiğimde ise Resim-6 da bulunan hata ile karşılaşıyorum.

6_connect_controller.JPG

 

İlgili sorunu tekrar müşteri destek hattına ilettiğimde M218 ve benzer şekilde M258 serisi PLC lerde belleklerinde dosya yapısı olmadığı, kendilerine aktarılan verilere gömülü bellek yaklaşımı kullandıkları cevabını aldım. Backup için özel bir cihaz olan "LOADER DEVICE" ı temin etmem gerektiği söylendi. Bu loader device ı temin edersem backup alabilecek miyim ve loader device a bağlanmam için somachine in hangi versiyonunu kurmam gerekiyor?

 

Sorunun çözümü konusunda yardımcı olabilir misiniz?

Solved! Go to Solution.

Labels
  • Machine Advisor
  • Makine PLC Programlama
Tags (3)
  • Tags:
  • english
  • M218
  • plc
Share
Reply

Accepted Solutions
ismailozinan
Ensign ismailozinan Ensign
Ensign
‎2020-06-18 04:03 AM
5 Likes
2
784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-18 04:03 AM

Re: M218 controller back-up alma problemi

Merhaba,

M218 PLC den program çekmek sözkonusu değildir.Sadece TM2USBABDEV1 referanslı ürün ile cihazın içindeki hex kodunu çekip yeni bir M218 plc ye kopyalamanız mümkün olabilir.

Linkteki dökümanın 180.sayfasında gösterildiği üzere programcının yazdığı kodu programlama dili şeklinde https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=Programming+Guide_E... görerek upload edemiyoruz.

 

application source
The application source file can be uploaded to the PC to reopen a SoMachine
project. This source file can support a full SoMachine project (for example, one that
includes HMI application).

 

Iyi Çalışmalar,

Saygılarımla

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
3 Replies 3
ismailozinan
Ensign ismailozinan Ensign
Ensign
‎2020-06-18 04:03 AM
5 Likes
2
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-18 04:03 AM

Re: M218 controller back-up alma problemi

Merhaba,

M218 PLC den program çekmek sözkonusu değildir.Sadece TM2USBABDEV1 referanslı ürün ile cihazın içindeki hex kodunu çekip yeni bir M218 plc ye kopyalamanız mümkün olabilir.

Linkteki dökümanın 180.sayfasında gösterildiği üzere programcının yazdığı kodu programlama dili şeklinde https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=Programming+Guide_E... görerek upload edemiyoruz.

 

application source
The application source file can be uploaded to the PC to reopen a SoMachine
project. This source file can support a full SoMachine project (for example, one that
includes HMI application).

 

Iyi Çalışmalar,

Saygılarımla

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
esra
Crewman esra
Crewman
‎2020-06-18 10:01 PM
1 Like
1
736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-18 10:01 PM

Re: M218 controller back-up alma problemi

Merhaba;

 

Öncelikle cevabınız için teşekkür ederim. Bir sorum daha olacak. Bende bulunan So machine versiyonu 4.3. Loader device ın bu versiyonda çalışıp çalışmadığı konusunda bir bilgi var mıdır?

Tags (1)
  • Tags:
  • english
Share
Reply
ismailozinan
Ensign ismailozinan Ensign
Ensign
‎2020-06-19 01:44 AM
2 Likes
0
727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-19 01:44 AM

Re: M218 controller back-up alma problemi

Merhaba,

  Loader cihaz, software den bağımsız çalışan bir cihazdır. Loader kullanırken herhangi bir software kullanamazsınız. Loader, cihazdaki hex kodunu alır, yazılan programı görüntüleme yada programa mudahale etme imkanı, yada programda diagnostic imkanı sunmaz. 

 

Iyi calismalar,

Saygilarimla

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
ozgurturkel
Lieutenant ozgurturkel Lieutenant
6
SemihUygunturk
Ensign SemihUygunturk Ensign
2
MuhteremCayli
Ensign MuhteremCayli Ensign
2
sesa500295_brid
Ensign sesa500295_brid Ensign
2
MetinSakin
Ensign MetinSakin Ensign
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric