Posted: 2021-12-08 05:26 PM
Pagi, saya ada pertanyaan, saya pake MCB 20 A di 228 V, beban sudah sampai 5000 W lebih tapi MCB tidak trip. Apakah artinya MCB rusak? Terima kasih
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-11 07:49 AM
Hi Pak.
MCB 20 A tidak langsung trip di 4400 W , karena MCB menggunakan kurva trip C.
Menurut IEC 60364-4-43, MCB harus trip maksimal dalam waktu 1 jam ketika mencapai 1.45 x arus nominal.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-11 07:49 AM
Hi Pak.
MCB 20 A tidak langsung trip di 4400 W , karena MCB menggunakan kurva trip C.
Menurut IEC 60364-4-43, MCB harus trip maksimal dalam waktu 1 jam ketika mencapai 1.45 x arus nominal.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-12 10:59 PM
Ah baik, berarti MCB 20 A seharusnya akan trip maksimal 1 jam di 6,380 W ya. Terima kasih banyak atas informasinya Pak @HelvinHermanT !