Posted: 2021-07-12 06:33 AM
Malam, mau tanya, kapasitas MCCB/ACB dalam suatu panel induk (incoming) kekuatan sebenarnya berapa persen dari kapasitas MCCB/ACB tsb? Thanks.
Posted: 2021-07-13 09:08 PM
Hi Pak,
Menurut UL489, circuit breaker standar 80% rated. Artinya dalam disain untuk continous maupun uncontinous load, bisa menggunakan 80% rated load dari sebuah circuit breaker.
Jika membutuhkan 100% rated load dari circuit breaker, maka memerlukan paduan Circuit Breaker dan Enclosure (Panel Box) yang didisain baik sehingga bisa 100% rated load (tanpa menyebabkan panas berlebih).
Posted: 2021-07-13 09:08 PM
Hi Pak,
Menurut UL489, circuit breaker standar 80% rated. Artinya dalam disain untuk continous maupun uncontinous load, bisa menggunakan 80% rated load dari sebuah circuit breaker.
Jika membutuhkan 100% rated load dari circuit breaker, maka memerlukan paduan Circuit Breaker dan Enclosure (Panel Box) yang didisain baik sehingga bisa 100% rated load (tanpa menyebabkan panas berlebih).
Posted: 2021-07-14 02:35 AM
Terima kasih Pak @HelvinHermanT infonya.
Untuk 100% rated MCCB/ACB. apakah Schneider punya Pak?