Posted: 2021-11-15 05:58 AM . Last Modified: 2021-11-15 05:59 AM
Hi Pak, terima kasih pertanyaannya.
Mengenai Standar Panel Listrik untuk rumah sakit bisa kita lihat pada IEC IEC 60364-7-710 Edition 2.0 2021-05 Low-voltage electrical installations – Part 7-710: Requirements for special installations or locations – Medical locations.
Bisa dilihat pada ayat 7.10.51 :
710.51.101 Distribution boards
710.51.101.1 General
Distribution boards shall be in accordance with IEC 61439 (all parts).
Separate distribution boards shall be provided for the general power supply and the electric supply system for safety services.
710.51.101.2 Medical locations of group 2
Distribution boards for group 2 medical locations shall be installed in close proximity to the areas they serve and be clearly labelled. Distribution boards shall be installed outside the group 2 medical locations and should be safely secured against operation by unauthorized persons.
The medical IT distribution board should be located within 25 m of the area it serves. Leakage currents should be taken into consideration.
NOTE 1 The 25 m are related to possible capacitive leakage current.
Recommendations for the minimum distances from the isolating transformers of the medical IT system to the equipment used within the patient environment are shown in informative Annex B.
The distribution board should be easily accessible for maintenance and be located on the same level and within the same fire compartment as the load it serves.
NOTE 2 A distribution board for medical locations is one that fulfils the functions for the supplied medical location
area assigned to it and where the main power supply voltage is monitored for operating the change-over to the
electric supply system for safety services in accordance with 710.313.1.101 and 710.313.1.102.
Bisa disimpulkan bahwa Standar Panel Listrik untuk rumah Sakit adalah mengacu pada IEC 61439 (semua bagian) yang artinya menggunakan Panel Listrik yang memiliki uji tipe (Type Tested IEC 61439). Dalam hal ini bisa menggunakan Panel Listrik yang memiliki uji tipe dari Schneider Electric : Prisma iPM, Blokset & Okken.
Untuk lokasi Panel dalam radius 25 meter dari area yang di layani / di suplai dan pada lantai yang sama.
Posted: 2021-11-15 05:58 AM . Last Modified: 2021-11-15 05:59 AM
Hi Pak, terima kasih pertanyaannya.
Mengenai Standar Panel Listrik untuk rumah sakit bisa kita lihat pada IEC IEC 60364-7-710 Edition 2.0 2021-05 Low-voltage electrical installations – Part 7-710: Requirements for special installations or locations – Medical locations.
Bisa dilihat pada ayat 7.10.51 :
710.51.101 Distribution boards
710.51.101.1 General
Distribution boards shall be in accordance with IEC 61439 (all parts).
Separate distribution boards shall be provided for the general power supply and the electric supply system for safety services.
710.51.101.2 Medical locations of group 2
Distribution boards for group 2 medical locations shall be installed in close proximity to the areas they serve and be clearly labelled. Distribution boards shall be installed outside the group 2 medical locations and should be safely secured against operation by unauthorized persons.
The medical IT distribution board should be located within 25 m of the area it serves. Leakage currents should be taken into consideration.
NOTE 1 The 25 m are related to possible capacitive leakage current.
Recommendations for the minimum distances from the isolating transformers of the medical IT system to the equipment used within the patient environment are shown in informative Annex B.
The distribution board should be easily accessible for maintenance and be located on the same level and within the same fire compartment as the load it serves.
NOTE 2 A distribution board for medical locations is one that fulfils the functions for the supplied medical location
area assigned to it and where the main power supply voltage is monitored for operating the change-over to the
electric supply system for safety services in accordance with 710.313.1.101 and 710.313.1.102.
Bisa disimpulkan bahwa Standar Panel Listrik untuk rumah Sakit adalah mengacu pada IEC 61439 (semua bagian) yang artinya menggunakan Panel Listrik yang memiliki uji tipe (Type Tested IEC 61439). Dalam hal ini bisa menggunakan Panel Listrik yang memiliki uji tipe dari Schneider Electric : Prisma iPM, Blokset & Okken.
Untuk lokasi Panel dalam radius 25 meter dari area yang di layani / di suplai dan pada lantai yang sama.
Posted: 2021-11-17 07:10 PM
Ah, baik, berarti menggunakan panel dengan standard IEC 61439 ya Pak @HelvinHermanT . Terima kasih Pak atas informasinya!