Aflr singkatan apa ya?

Solved
WahyuSihotang
Crewman
Crewman
0 Likes
7
304

Aflr singkatan apa ya?

Siang, mau tanya, Aflr singkatan apa ya? Thanks


Accepted Solutions
taqin
Crewman Crewman
Crewman

Re: Aflr singkatan apa ya?

A : Authorized Personnel Only

F : Front Side

L : Lateral Side 

R : Rear

 

Kaitannya dengan IAC : Internal Arc Class

 

A-FLR = four sides protection = proteksi terhadap resiko Internal Arc (Ledakan dalam Panel) untuk 4 sisi Panel Tegangan Menengah

 

4 Sisi  :

 

Front = sisi bagian depan 

Lateral = sisi bagian samping Kiri dan samping Kanan

Rear = sisi bagian belakang

See Answer In Context

Tags (1)
7 Replies 7
HelvinHermanT
Commander Commander
Commander
0 Likes
6
301

Re: Aflr singkatan apa ya?

A-FLR menurut definisi IEC 62217-200 merupakan All Sided Protection for Users.

 

 

@taqin 

Tags (1)
taqin
Crewman Crewman
Crewman

Re: Aflr singkatan apa ya?

A : Authorized Personnel Only

F : Front Side

L : Lateral Side 

R : Rear

 

Kaitannya dengan IAC : Internal Arc Class

 

A-FLR = four sides protection = proteksi terhadap resiko Internal Arc (Ledakan dalam Panel) untuk 4 sisi Panel Tegangan Menengah

 

4 Sisi  :

 

Front = sisi bagian depan 

Lateral = sisi bagian samping Kiri dan samping Kanan

Rear = sisi bagian belakang

Tags (1)
WahyuSihotang
Crewman
Crewman
0 Likes
4
289

Re: Aflr singkatan apa ya?

Sore, terima kasih atas penjelasan lengkapnya Pak @HelvinHermanT , Pak @taqin  
Kalau MCSet Aflr ngga Pak?

HelvinHermanT
Commander Commander
Commander
0 Likes
3
269

Re: Aflr singkatan apa ya?

MCSet mempunyai 2 macam proteksi: A-FL atau A-FLR.

 

@taqin 

Tags (1)
WahyuSihotang
Crewman
Crewman
0 Likes
2
264

Re: Aflr singkatan apa ya?

Kalau A-FL apa ya Pak?

Tags (1)
HelvinHermanT
Commander Commander
Commander
0 Likes
1
259

Re: Aflr singkatan apa ya?

Hi Pak,

 

Seperti dijelaskan diatas :

 

A-FL = Front & Lateral. Maksudnya Proteksi dari sisi depan (Front) dan sisi kiri kanan  (Lateral).

 

Semoga membantu,

WahyuSihotang
Crewman
Crewman
0 Likes
0
256

Re: Aflr singkatan apa ya?

Siap, paham Pak! Terima kasih banyak atas informasinya Pak @HelvinHermanT dan Pak @taqin 