Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
The impact of harmonic currents (THDi) on the low voltage distribution circuits
EcoStruxure Power Design Forum
Schneider Electric support forum to share knowledge about installation and usage for Electrical Network Design and Calculation Software (Ecodial, Ecostruxure Power Design).
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-2303:45 AM. Last Modified: 2021-01-0305:23 PM
The impact of harmonic currents (THDi) on the low voltage distribution circuits
Introduction :
The third harmonic content of the line current is the ratio of the "third harmonic" and the fundamental (first harmonic), and this is expressed in percentage (%). let us see its impact on the low voltage distribution circuits.
Harmonic Currents :
This is to cover the situation where there is current flowing in the neutral of a balanced three-phase system
Such neutral currents are due to the line currents having a harmonic content, which does not cancel in the neutral. The most significant harmonic which does not cancel in the neutral is usually the third harmonic.
The magnitude of the neutral current due to the third harmonic may exceed the magnitude of the power frequency line current. In such a case, the neutral current will have a significant effect on the current carrying capacity of the cables in the circuit.
Kindly be notes that, when the harmonic content is more than 33 % then the cable size determining is based on the neutral current.
Conclusion :
The THDi of the circuit leads to bring attention in sizing the neutral conductor, and based on its value (>33%) the neutral become the size determining conductor. In some case, neutral conductor is bigger than the line conductor.