Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Different between integrated and separated thermal protection
EcoStruxure Power Design Forum
Schneider Electric support forum to share knowledge about installation and usage for Electrical Network Design and Calculation Software (Ecodial, Ecostruxure Power Design).
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-2708:14 AM
Different between integrated and separated thermal protection
Dear Experts ,
I made a small project in Ecodial for a three-phase motor 90KW and i see when i select integrated thermal protection the cross-section of cable is 1x50 but when i changed to the separated thermal protection the cross-section of cable become 1x70 as shown in attached pictures .
Kindly can someone explain to me why there is a difference between the two results? .
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-2709:55 AM
Hi Omar,
The long time setting of the Integrated Thermal relay Circuit breaker is 170A. And the cable is sized for 170A which is (1X50sq.mm). But for Separated Thermal relay Circuit breaker it is 220A. So that particular cable is sized for 220A(1X70sq.mm). Refer the properties tab on Circuit breaker selected to get the Long time setting.