An example for 'determining the smallest allowable cross-sectional area of circuit conductors.'
From the available inputs;
let us see how to determine the 'smallest allowable cross sectional area' of the circuit conductors.
Available inputs;
Load Current |
200 A |
THDi |
48 % |
Conductor Insulation* |
XLPE |
Conductor Type |
Multi-Core Cable |
Conductor Material* |
Copper |
Installation |
Directly in Ground |
Soil Resistivity* |
2 Km/w |
Soil Temperature* |
40*C |
*Some of the inputs are assumed to provide in this example; and they were neither received from the user, nor from the environment.
Procedure:
- Determinant conductor : Neutral
As the THDi is > 33 % (that is THDI = 48 %). So, the Size-determining" live conductor is Neutral
- Neutral Current : 3 × 0.48 × 200 = 288 A
- Correction factor K3 : The factor based on the overload protection device.
This circuit is assumed to be protected by the circuit-breaker.
So that the K3 =1.0
- F1 Temperature : Table B.52.15
For 40°C and with the insulation XLPE. F1 = 0.85
- Installation method : 72 (Sheathed single-core or multi-core cables direct in the ground - without added mechanical protection) Reference method : D2
- F2 Group : Table B.52.18
There is no additional touching circuits i.e. total no. of circuits is 1
F2group = 1.00
- Correction factor F3 : Table (E.52.1)
THDI >45 % = THDI = 48 % à f3NeutralTHDI = 1.00
- F3RSoil : Table B.52.16
Installation method = in Ground -> Rth = 2.0 K.m/w
f3RthSoil = 1.12
- K user = 1.0
Correction factor f
f = 0.85 × 1.00 × 1.00 × 1.05 × 1.00 = 0.952
The overall correction factor is determined by multiplying all 'the available correction factors."
Theoretical Iz’ = (K3 x IB) / (F x N live) = (1.0 x 288) / (0.952 x1) = 302.52 A = 303 A
The conductor selection is done from the given Table B.52.5 Column 8
185 mm2 will be able to carry 324 Amps
240 mm2 will be able to carry 375 Amps
Considering the +5% of tolerance, It would be recommended to consider the size as 185 mm²
K3(Correction Factor based on Protection Device) |
1 |
F1(Correction Factor based on Temperature) |
0.85 |
F2(Correction Factor based on Group of conductors) |
1 |
F3(Correction Factor based on THDi) |
1 |
F3(Correction Factor based on Soil Resistivity) |
1.05 |
K user(Correction Factor defined by the user) |
1 |
|
|
Iz’(A) Theoretical |
303 A |
Iz (A) considered from the table |
324 A |
Theoretical cross sectional area Ph (mm²) |
1 x 185 mm² |
Theoretical cross sectional area Neutral (mm²) |
1 x 185 mm² |
Theoretical cross sectional area PE (mm²) |
1 x 95 mm² |
- Labels:
-
Power Distribution Software
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:32 AM
That's really informative answer.
Thanks.
Link copied. Please paste this link to share this article on your social media post.