dear expert,
Where could I find the document for detail function for each report? For example, in capacity history report, there is one checkbox called 'ambient temperature', and we found that it has only 1 data each day and we don't know where DCO get it and how it was generated. Because we have more than 10 temperature sensors in one room and all data uploaded. And I don't know how to explain this to the customer. This situation also happens on some other reports.
Best Regards,
Ziqiang
(CID:118001107)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:50 PM
This answer was originally posted on DCIM Support by Jef Faridi on 2017-05-05
Hi Ziqiang,
Please see the following page, that contains full description of capacity history data:
Capacity history KPI description
Kind regards
(CID:118001126)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:50 PM
This answer was originally posted on DCIM Support by Jef Faridi on 2017-05-05
Hi Ziqiang,
Please see the following page, that contains full description of capacity history data:
Capacity history KPI description
Kind regards
(CID:118001126)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:50 PM
This comment was originally posted on DCIM Support by ziqiang wu on 2017-05-08
Hi Jef,
Thank you for the answer. The customer is asking, just for ambient temperature, could we give a description how this value be calculated because they have encountered some unreasonable values in the report ( see attached). They have some values which is lower than 0 degree in Celsius.
Thanks,
Ziqiang
(CID:118001540)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:50 PM
This comment was originally posted on DCIM Support by Jef Faridi on 2017-05-11
Hi Ziqiang,
The ambient temperature (sort of average temperature of the room) is based on the 2D cooling 'calculations'/algorithm. It is really just a rough estimation of the temperature of air that cannot be accounted for by rack exhausts or cooler supplies. However, the ambient temperature might be affected by manual settings such as rack & CRAC's cooling settings,
Kind regards
(CID:118003641)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:50 PM
This comment was originally posted on DCIM Support by ziqiang wu on 2017-05-17
Thanks Jef,
I have created a new thread for the ambient temperature question. The customer is not quite buy in this explain. They want some detail explanation. Could you help?
The following is on:
Thanks a lot,
Ziqiang
(CID:118622066)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:50 PM . Last Modified: 2023-10-22 09:39 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.