EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:54 PM . Last Modified: 3 weeks ago
I would like to integrate our Easy UPS 3S into DCE. I have imported it but it appears as an SNMP Device. Is there a MIB file I can download so DCE understands what the unit is?
(CID:152080358)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:55 PM . Last Modified: 3 weeks ago
Dear Mario,
MIB file can not be uploaded in DCE software directly. I have attached the Easy UPS 3S SNMP card DDF file. Please check if you are able to see the device sensors after uploading the attached DDF file.
Please let me know if you still need MIB file. I can provide it to you.
(CID:152080398)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:55 PM . Last Modified: 3 weeks ago
Thank you Balaraman. I assume you upload the file into DCE via the Device / SNMP Device Communication Settings section?
It recognises it as a UPS now.
Thank you for your help.
(CID:152570129)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:55 PM . Last Modified: 3 weeks ago
Thanks for the update Mario! To import: Main menu->Device->SNMP Device Communication Settings->Device Definition Files->Add/Update Definitions
(CID:152570131)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:55 PM . Last Modified: 2023-10-22 09:39 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.