I would like to integrate our Easy UPS 3S into DCE. I have imported it but it appears as an SNMP Device. Is there a MIB file I can download so DCE understands what the unit is?
(CID:152080358)
This answer was originally posted on DCIM Support by Balaraman Jagadeesan on 2019-12-02
Dear Mario,
MIB file can not be uploaded in DCE software directly. I have attached the Easy UPS 3S SNMP card DDF file. Please check if you are able to see the device sensors after uploading the attached DDF file.
Please let me know if you still need MIB file. I can provide it to you.
(CID:152080398)
This comment was originally posted on DCIM Support by Mario Piazzese on 2019-12-02
Thank you Balaraman. I assume you upload the file into DCE via the Device / SNMP Device Communication Settings section?
It recognises it as a UPS now.
Thank you for your help.
(CID:152570129)
This comment was originally posted on DCIM Support by Balaraman Jagadeesan on 2019-12-02
Thanks for the update Mario! To import: Main menu->Device->SNMP Device Communication Settings->Device Definition Files->Add/Update Definitions
(CID:152570131)