Sign In Help
Schneider Electric
HelpLogin / Register

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Communities
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: vCenter integration issue - cannot connect to vCenter
Community Menu
  • Forums
    • By Topic
        • EcoStruxure Building
          • Field Devices Forum
        • EcoStruxure Power & Grid
          • Metering & Power Quality
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Automation Forum
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
          • Motorabgangstechnik & Antriebstechnik Forum
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Solutions for Motor Management
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
          • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
        • Power Distribution NEMA
          • US Utility Forum
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure Building
        • Field Devices Forum
      • EcoStruxure Power & Grid
        • Metering & Power Quality
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Automation Forum
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
        • Motorabgangstechnik & Antriebstechnik Forum
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Solutions for Motor Management
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
        • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Power Distribution NEMA
        • US Utility Forum
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • EcoStruxure Power & Grid
          • Backstage Access Resources
        • Industrial Automation
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
          • UK&I Residential and Commercial Electrical Distribution
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
          • Solutions for eMobility
          • Digital Hospital Solutions – UK&I
        • Knowledge Center
          • Industrial Automation How-to videos
          • Digital E-books
          • Success Stories Corner
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
        • Retail
          • Solutions for eMobility
        • Retail
          • Digital Hospital Solutions – UK&I
      • EcoStruxure Power & Grid
        • Backstage Access Resources
      • Industrial Automation
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
        • UK&I Residential and Commercial Electrical Distribution
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
        • Solutions for eMobility
        • Digital Hospital Solutions – UK&I
      • Knowledge Center
        • Industrial Automation How-to videos
        • Digital E-books
        • Success Stories Corner
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
      • Retail
        • Solutions for eMobility
      • Retail
        • Digital Hospital Solutions – UK&I
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
52940members
Join Now
248289posts
Join Now

vCenter integration issue - cannot connect to vCenter

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 08:35 PM
0 Likes
4
137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 08:35 PM

vCenter integration issue - cannot connect to vCenter

This question was originally posted on DCIM Support by Mate Fekete on 2019-07-11


I have DC version 8.2.12 and using couple vCenter integration. Each and every time when I start DCO desktop client I get this error message:

I go to External System Configuration into the same vCenter settings and click on Test button:

I have 7 other vCenter server in the system and crosschecked all settings and did not found any problem. Of course above mentioned vCenter is available and tested user credentials with a login which works fine.

What is the problem?

 

(CID:147194428)

Labels
  • Data Center Operation
Share
  • All forum topics
  • Previous Topic
  • Next Topic
4 Replies 4
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 08:35 PM
0 Likes
0
137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 08:35 PM

Re: vCenter integration issue - cannot connect to vCenter

This comment was originally posted on DCIM Support by Jef Faridi on 2019-07-15


Hi Mate,

Can I ask for server logs? to see if it contains useful info, thanks.

Kind regards

(CID:147195125)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 08:35 PM
0 Likes
0
137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 08:35 PM

Re: vCenter integration issue - cannot connect to vCenter

This comment was originally posted on DCIM Support by Mate Fekete on 2019-07-18


Hi Jef,

Servers log and latest backup has been uploaded to appbox.

Thanks.

(CID:147196366)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 08:35 PM
0 Likes
0
137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 08:35 PM

Re: vCenter integration issue - cannot connect to vCenter

This answer was originally posted on DCIM Support by Jef Faridi on 2019-08-06


Hi Mate,

Unfortunately I could not see error entries in the latest log entries, so it is not clear to me why you might be seeing the warning message. I will post you a direct email soon, thanks.

Kind regards

(CID:147202243)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 08:35 PM
0 Likes
0
137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 08:35 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
46
APC_Steve
Lt. Commander APC_Steve Lt. Commander
26
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
14
JLehr
Lieutenant JLehr Lieutenant
7
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2021, Schneider Electric