EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:39 PM . Last Modified: 3 weeks ago
Dear Team,
I was receiving fake notification from Symmetra PX 160, i.e Ups battery charging in 100% and showing run-time of 110min on current load but i receive email notification of 12min. So i am trying to update its NMC firmware but it was showing error, Please find the attached FW which i was trying to update, error is below
apc_hw05_aos650_sy3p650_bootmon108.rar
(CID:137727444)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:39 PM . Last Modified: 3 weeks ago
Dear Muhammad Shahzad,
Make firmware flashing, you should always be the last thing.
I am sure, that the reason for the false alert is quite different.
The more information you provide, the faster and better your help will be 😀.
With respect.
(CID:137727557)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:39 PM . Last Modified: 3 weeks ago
Dear spezialist,
I receive alert by SMS from DCE software.
Currently data logs are not available but NMC hardware/software revisions are below.
(CID:137727618)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:39 PM . Last Modified: 3 weeks ago
Dear Muhammad Shahzad,
From your comments:
I receive alert by SMS from DCE software.
Why did you decide that a flashing will help you? You use the old first generation NMC. What version of the new firmware did you want to flash?
The event-log from NMC is available for you?
Please show the screenshot of the report on sensor UPS runtime from DCE software for the period where you discovered a false alert.
With respect.
(CID:137727631)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:39 PM . Last Modified: 3 weeks ago
Dear Muhammad Shahzad,
Please tell us if you could solve your problem or not?
With respect.
(CID:137729833)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:39 PM . Last Modified: 3 weeks ago
Dear spezialist
I have check eventlogs but didnt found low battery logs in the history. Customer wanted to upgrade NMC firmware but i am unable to do this due to above error. Please share HW compatible FW of NMC.
Details are already shared above.
Thanks
MS
(CID:137730466)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:39 PM . Last Modified: 3 weeks ago
Dear Muhammad Shahzad,
From your comments:
...Customer wanted to upgrade NMC firmware but i am unable to do this due to above error.
From your screenshots it follows, that you are using the old first generation NMC. Accordingly, you can upgrade the firmware only to version SFSYPX2377_390 dated 07/29/2015 (Network Management Card v3.7.7 Firmware Executable for Symmetra PX 48; 96; 100; and 160 kW Systems). You can download this firmware from the https://www.apc.com/us/en/tools/download/ resource.
Try it, and you will succeed.
With respect.
(CID:137730735)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:39 PM . Last Modified: 3 weeks ago
Dear spezialist
I didnot found Firmware for Symmetra PX 160. Can you please share me in zip file or directly download link.
Regards
MS
(CID:138811245)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:40 PM . Last Modified: 3 weeks ago
Dear shahzad.engr123,
The above firmware can be downloaded from the link: https://download.schneider-electric.com/files?p_Archive_Name=MFOI-9LKKLD.zip&p_enDocType=Software+-+...
With respect.
(CID:138811335)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:40 PM . Last Modified: 3 weeks ago
Dear spezialist
Thank you for your usual support
(CID:138811584)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:40 PM . Last Modified: 3 weeks ago
Ok, thanks for the good feedback 😀.
(CID:138811630)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:40 PM . Last Modified: 3 weeks ago
Dear spezialist
I didnot found Firmware for Symmetra PX 160. Can you please share me in zip file or directly download link.
Regards
MS
(CID:138811243)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 03:40 PM . Last Modified: 2023-10-22 09:37 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.