Hi, We have had a new SNMP DDF created for some Airedale chillers, this has been uploaded to the server and displays the sensors as i would expect. The issue i have is we have other Denco chillers on the system which have now decided to use the Airedale DDF and now do not show the sensors correctly. Both chillers are using Carrel network cards but looks like maybe OID references are different accross the 2 devices. How can i force the denco chillers to use the original DDF on the server? Kind Regards
(CID:146671128)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:30 PM
This answer was originally posted on DCIM Support by Cory McDonald on 2019-07-10
Stephen,
I believe that Carrel network cards allow you to define the SysOID in their web interface. I am wondering if they are set to the same thing for the two different device manufacturers. One of them may need to be changed an a new or updated DDF based off of that one, as the SNMP OIDs should change when the SysOID is changed.
Regards,
Cory
(CID:147194016)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:30 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-07-09
Hi Stephen,
Do you have any information on the card type used in these systems? The reason I ask is I've seen a similar issue in the past with Uniflair devices that use the old PCOWeb cards. There was no specific OID that could be used to identify the different devices so it would simply use the first Uniflair DDF it found. In that instance, there were 2 ways around this. 1 is to use only one DDF and build a second DCE VM for the other device / model (cost prohibitive) and the second was to use Modbus instead of SNMP. If you look in the 2 DDF files, I'm assuming the SNMP OIDs are the same which would point to something like this being the cause.
Steve
(CID:146671200)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:30 PM
This comment was originally posted on DCIM Support by Steven Marchetti on 2019-07-10
Oh, looks like I missed the mention of the Carel cards (which is the PCOWeb card) it looks like that IS the issue.
(CID:147194113)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:30 PM
This answer was originally posted on DCIM Support by Cory McDonald on 2019-07-10
Stephen,
I believe that Carrel network cards allow you to define the SysOID in their web interface. I am wondering if they are set to the same thing for the two different device manufacturers. One of them may need to be changed an a new or updated DDF based off of that one, as the SNMP OIDs should change when the SysOID is changed.
Regards,
Cory
(CID:147194016)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:31 PM
This comment was originally posted on DCIM Support by Stephen Gilbert on 2019-07-11
Hi Thank you for the information, i will look into this and comment back with the results 😀
Kind Regards
Steve
(CID:147194611)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:31 PM
This comment was originally posted on DCIM Support by Stephen Gilbert on 2019-07-12
Hi the system OID is set to 1.3.6.1.4.1.8072.3.2.10 is it as easy as changing the 1st number to 2 and then edit the DDF so each OID starts with 2?
Kind Regards
Steve
(CID:147194732)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:31 PM
This comment was originally posted on DCIM Support by Jake Hiltz on 2019-07-12
Hi Steve,
Do not change any OIDs in the DDF for sensors or alarms. In the DDF, near the top is a an XML element "oidMustMatch" or "oidMustExist". This is what defines which DDF should be used for a device. So, as Cory recommended, if you can make the system OID unique on the device, then you can update the DDF to look for it. When changing the system OID, make sure it is something that is unique. I would recommend adding another period plus some number(s). This way it still follows the convention for system OIDs and is still clearly identifiable as a Carel web card. Let's say you change the system OID from "1.3.6.1.4.1.8072.3.2.10" to " 1.3.6.1.4.1.8072.3.2.10.0" . Then, in the DDF, you would need to add this:
<oidMustMatch ruleid="sysobjidtest" oid=".1.3.6.1.2.1.1.2.0">
<valueList>
<value>.1.3.6.1.4.1.8072.3.2.10.0</value>
</valueList>
</oidMustMatch>
If you already have an "oidMustMatch" element, you can just update it. If not, you can add this.
Does that make sense? Please let us know how it works for you.
Thanks,
Jake
(CID:147194899)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:31 PM
This comment was originally posted on DCIM Support by Stephen Gilbert on 2019-07-15
Hi Jake,
Thank you for the information. i have done as you said and changed the system OID to 1.3.6.1.4.1.8072.3.2.10.1 and amended the oidMustMatch rule to match this. the device now discovers as the correct device but i am getting no sensors in my sensor list. The programmed alarms are visible in the alarm config tab of DCE though so it seems to have half worked....
Kind Regards
Steve
(CID:147195174)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:31 PM
This comment was originally posted on DCIM Support by Stephen Gilbert on 2019-07-15
Sorry ignore that last comment, the sensors have now populated, took about 20 mins for the sensors to appear but all is now displaying as i would expect. thank you for you assistance.
Thanks
Steve
(CID:147195232)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:31 PM
This answer was originally posted on DCIM Support by Jake Hiltz on 2019-07-10
Carel pCOWeb cards do not provide enough information to determine what type if device it is. This is partly because with SNMP, the standard is that OIDs have one and only one meaning. Carel PCO cards violate this standard and re-use the same OIDs to mean different things. Because of this, DCE can only have 1 device that uses a Carel PCO card.
(CID:147194021)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:31 PM . Last Modified: 2023-10-22 09:36 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.