Hello,
we have two Chiller units, both are showing online on DCE devices window, with the IPs 192.168.0.X.
If we double-click any of them, it open their webpage where I click "Go to Administrator page" link then this error comes up (refer to the attachment).
If we try it on a browser window it doesn't respond, but my client doesn't want to add routing for 192.168.0.* they want to open the webpages for both devices on DCE by avoiding this error.
And if I open chiller's webpage by connecting directly to APC switch (which is connected with DCE) it works perfectly fine.
Can anybody help ?
(CID:105474452)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:23 AM . Last Modified: 2 weeks ago
Hi Raza,
If I am correct on what is happening, the easiest resolution here is to put the device on the DCE public LAN. What I'm thinking is happening here is that the browser is trying to download an active-X control or some other control that needs to be downloaded but can't. K-base FA239966 notes this issue. As for routing to the private LAN from the public, that can cause issues as well and is unsupported.
Steve
(CID:105474465)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:22 AM . Last Modified: 2 weeks ago
What model are the chiller?. You need a ddf file for it, to be connect to DCE
(CID:105474458)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:22 AM . Last Modified: 2 weeks ago
well I don't know the model but its showing "Normal" status in DCE, & also showing device sensors by right-clicking. Read the error msg maybe then you can get what I'm asking.
(CID:105474464)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:23 AM . Last Modified: 2 weeks ago
Hi Raza,
If I am correct on what is happening, the easiest resolution here is to put the device on the DCE public LAN. What I'm thinking is happening here is that the browser is trying to download an active-X control or some other control that needs to be downloaded but can't. K-base FA239966 notes this issue. As for routing to the private LAN from the public, that can cause issues as well and is unsupported.
Steve
(CID:105474465)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:23 AM . Last Modified: 2 weeks ago
if I m correct you need to check the proxy and fire wall may be it help you out on this issue ..
(CID:106202902)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:23 AM . Last Modified: 2023-10-31 11:30 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.