I am first time trying to setup netbotz 450, but i cannot add smoke on the device. anyone can help me?
(CID:116362683)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:44 PM . Last Modified: 2 weeks ago
😀, I did not ask in vain: "Are any thresholds already set on these temperature sensors or not?"
You have a enabled humidity range threshold for this temperature sensor: if the humidity is less than 70% or more then 80%, then an alarm is triggered, which is displayed as a flushed error:
Either disable/remove this range threshold, or change its value to reasonable limits, for example, from 30 ... 35% to 65...70%.
With best regards.
(CID:116364186)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:43 PM . Last Modified: 2 weeks ago
Hi c.lor,
Describe, please, your problem in more detail: what messages when adding a sensor appear, for example?
Show, please, a screenshot of your actions with this sensor type.
With best regards.
(CID:116362773)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:43 PM . Last Modified: 2 weeks ago
Please find it after I login with Advance view 4.5.4.
(CID:116362788)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:43 PM . Last Modified: 2 weeks ago
First, try to disconnect physically a failure sensor (if it is still connected), and then to remove it from the Advanced View (from the shortcut menu). Only after successful removing a failure sensor try to connect a sensor again physically.
In more detail about the same problem it is possible to read here .
With best regards.
(CID:116362908)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:43 PM . Last Modified: 2 weeks ago
I am trying to configure but it have error like picture. and I also trying to change from F to C but still not working.
(CID:116363895)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:43 PM . Last Modified: 2 weeks ago
Hi c.lor,
First, what type of temperature sensors you connect to the NetBotz and in which ports (their numbers)? Are any thresholds already set on these temperature sensors or not?
Try physically to disconnect these temperature sensors, then remove them from the Advanced View window, and then physically reconnect to the NetBotz.
Secondly, the language localization of information display in the Advanced View software is tied to the language locale of your session in the OS. Hence the question: what is your OS on the PC and what language locale is setup in your session?
Question three: how do you connect using the Advanced View to the NetBotz device? Directly (by the IP address of NetBotz) or via the SOCKS proxy on the DCE server?
With best regards.
(CID:116364007)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:43 PM . Last Modified: 2 weeks ago
(CID:116364032)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:43 PM . Last Modified: 2 weeks ago
the cable sensor it coming by default I think it 3 m. right now I change from F to C is working. but the humidity still error. please find picture in attached.
(CID:116364168)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:44 PM . Last Modified: 2 weeks ago
Now I am deleted all and re-connect physical again, it found like this picture, so that's mean it working?
(CID:116362893)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:44 PM . Last Modified: 2 weeks ago
I congratulate you: You made it 😀. On a screenshot Smoke sensor in the normal state (No Smoke) is visible. It was necessary only to setup threshold value and response of the NetBotz device to its actuating (to send the alarm e-mail, SMS or to enable Beacon , etc.)
With best regards.
(CID:116362907)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:44 PM . Last Modified: 2 weeks ago
may you guide me how to enable? do you have another document relate with smoke, I am trying to find on google and apc but not found correct.
(CID:116362912)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:44 PM . Last Modified: 2 weeks ago
😀, I did not ask in vain: "Are any thresholds already set on these temperature sensors or not?"
You have a enabled humidity range threshold for this temperature sensor: if the humidity is less than 70% or more then 80%, then an alarm is triggered, which is displayed as a flushed error:
Either disable/remove this range threshold, or change its value to reasonable limits, for example, from 30 ... 35% to 65...70%.
With best regards.
(CID:116364186)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:44 PM . Last Modified: 2 weeks ago
With Smoke sensor delivers only the short instruction for initial hardware installation 😀.
Concerning initial configuring of NetBotz it is possible to read here:
I have no Smoke sensor, but if it is very short, then here several sequential pictures:
With best regards.
(CID:116921079)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:44 PM . Last Modified: 2 weeks ago
Ok, what is the approximate length of the temperature sensor cable? Is there an extension cable?
If you locale is U.S. then it's normal, the temperature should be in Fahrenheit 😀.
Try to change another locale or: to change the readings on Celsius, try in Windows 10 to go to Control Panel -> Region -> in Formats tab -> Additional settings... -> Measurement system: Metric:
With best regards.
(CID:116921075)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:44 PM . Last Modified: 2 weeks ago
now I can back to working. I have another case with GSM modem connect to USB A. but I don't know how to test and getting working with netbotz. can you advise I need to create new case or can used with this exiting?
(CID:116364221)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:44 PM . Last Modified: 2 weeks ago
On this question there are already several open topics, for example:
But in this question should be guided Version 3 Netbotz modem support and this manuals for NetBotz-450 hardware:
I.e., NetBotz devices unfortunately support a very limited number of USB modems. It all depends on what kind of modem you have?
I am always glad to help.
(CID:116364256)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:45 PM . Last Modified: 2023-10-22 09:33 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.