Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • lost webmin details DCO 8.2.2
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49248members
Join Now
242460posts
Join Now

lost webmin details DCO 8.2.2

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:34 PM
0 Likes
6
41
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:34 PM

lost webmin details DCO 8.2.2

This question was originally posted on DCIM Support by mike sutton on 2019-01-28


Hi I have a client running DCO 8.2.2 who has lost the Webmin password and more than likely there username as well i know we could recover them in earlier versions but that doesn't seem to work with Centos 7 has anyone got a workaround for this?? tried pressing e and editing the linux16 entry from "root ro" to "root rw init=/sysroot/bin/sh" then run  but still wont let me run the /etc/passwd cmd

I can log in using my user credentials but unable to sudo or run passwd as I've not got root access!

TIA

Mike

 

(CID:138810321)

Solved! Go to Solution.

Labels
  • Data Center Operation
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:35 PM
0 Likes
4
41
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:35 PM

Re: lost webmin details DCO 8.2.2

This answer was originally posted on DCIM Support by Jef Faridi on 2019-01-28


Hi Mike,

Resetting user password  on the sever is described here:

Resetting user password on the DCO server

if you/customer do not recall the user name, after the step 4. (eg. 4. When you see Rescue Mount, press <return> and type chroot /mnt/sysimage.) type:

less /etc/passwd

and look for the created user name - in the following screen shot my test user "apc" is highlighted:

then continue the password reset for this user (per instructions)...

Kind regards

(CID:138810350)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
6 Replies 6
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:35 PM
0 Likes
4
42
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:35 PM

Re: lost webmin details DCO 8.2.2

This answer was originally posted on DCIM Support by Jef Faridi on 2019-01-28


Hi Mike,

Resetting user password  on the sever is described here:

Resetting user password on the DCO server

if you/customer do not recall the user name, after the step 4. (eg. 4. When you see Rescue Mount, press <return> and type chroot /mnt/sysimage.) type:

less /etc/passwd

and look for the created user name - in the following screen shot my test user "apc" is highlighted:

then continue the password reset for this user (per instructions)...

Kind regards

(CID:138810350)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:35 PM
0 Likes
0
41
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:35 PM

Re: lost webmin details DCO 8.2.2

This comment was originally posted on DCIM Support by mike sutton on 2019-01-29


Hi Jef,

I have carried this out no problems thanks however now i cant access the web client or DCO Client i can ping the IP but when i try to log on it says connection refused!

is there anyway i can check services through the server?

Cheers,

 

Mike

(CID:138810988)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:35 PM
0 Likes
0
41
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:35 PM

Re: lost webmin details DCO 8.2.2

This comment was originally posted on DCIM Support by Jef Faridi on 2019-01-29


Hi Mike,

Perhaps (only guessing) the application is not ready yet.

Log in to server Webmin interface (https://<server IP>:10000), StruxureWare DC Operation > Status and see if the application is running.

Kind regards

(CID:138811001)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:35 PM
0 Likes
0
41
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:35 PM

Re: lost webmin details DCO 8.2.2

This comment was originally posted on DCIM Support by mike sutton on 2019-01-29


It shows the following tried rebooting but no luck?

(CID:138811013)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:35 PM
0 Likes
0
41
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:35 PM

Re: lost webmin details DCO 8.2.2

This comment was originally posted on DCIM Support by Jef Faridi on 2019-01-30


Hi Mike,

I think in this case fast and reliable solution can be a clean installation of DCO and then restoring the latest "good" backup file.  Backup files are usually located in /data/backup folder.

PS: it is recommended to go for the latest version of DCO (currently 8.2.12)

Kind regards

(CID:138811341)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:35 PM
0 Likes
0
41
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:35 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric