Dear guys,
I have a Netbotz 570 which has disabled the Scanned Devices icon and it not appeat the Device Crawlers icon. How can I activate these options?
Best regards,
Enric Climent
(CID:105461490)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:48 PM
This answer was originally posted on DCIM Support by Balaraman Jagadeesan on 2016-01-27
Dear Enric,
In order to enable "Scanned Devices" option on Advance View of Netbotz, you need to activate NBWN0006 - NetBotz Device Monitoring (Five Nodes) Pack License key.
http://www.apc.com/shop/gb/en/products/NetBotz-Device-Monitoring-Five-Nodes-Pack/P-NBWN0006
From Netbotz 570 User Manual:
The Scanned Devices icon is only available with the purchase of the 5-node Scanner.
Scanned devices are SNMP targets that are monitored by the NetBotz appliance. You can monitor status information for up to five remote SNMP targets such as servers, routers, and switches as well as APC devices such as APC UPSs and APC Rack Power Distribution Units (PDUs). When you add SNMP targets, each target appears in the Navigation pane. Once added, you can set thresholds, monitor alerts, and graph reported data. For APC devices, at user-configurable intervals, the appliance retrieves sensor information specific to the APC device.
Regards,
Bala
(CID:105461494)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:48 PM . Last Modified: 2023-10-31 11:05 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.