Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: how do I create an alarm to show the ups has no input power
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51071members
Join Now
245140posts
Join Now

how do I create an alarm to show the ups has no input power

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:10 PM
0 Likes
5
193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:10 PM

how do I create an alarm to show the ups has no input power

This question was originally posted on DCIM Support by Ric Turner on 2019-10-30


We're trying to create a very simple alarm that will notify us when power is lost and the UPS switches over to "on battery" state, and then another that will notify us when the power is restored and the UPS returns to an "off battery" state.  Unfortunately, after nearly a week a searching, reading, and searching and reading MORE...we still can't find any kind of instructions to do this specifically.  We've viewed more than a dozen videos, but none of them show us how to do this particular thing.  For example, we watched a video called "Creating and Managing Thresholds in StruxureWare Data Center Expert", and it's a Schneider video.  The problem is, the video shows how to create a temperature threshold, and this sensor is found quite easily.  When we follow those instructions, we don't see anything close to resembling what we want to do.  We can see where a Schneider technician added a "state" sensor for our Galaxy 4000 for "On Battery", but we can't figure out how to do this for all our other UPS devices.  Can anyone graciously direct us to a video - or any other tutorial - that will show us how to add a "state" threshold for On Battery (and then Off Battery)?  It shouldn't be this difficult and convoluted, but here we are...

(CID:151061493)

Labels
  • DCIM Support
Share
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:10 PM
0 Likes
2
193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:10 PM

Re: how do I create an alarm to show the ups has no input power

This answer was originally posted on DCIM Support by Jonathan Gould on 2019-10-30


Hey Rick, this should be able to be done by going to the 'Alarm Configuration' view pane.  From there you should see a list of devices on the left and two view tabs to right (Threshold Alarm Configurations and Device Alarm Configurations).  In the list of devices on the left type 'UPS' into the search box at the top and it should sort to all of your UPS.  

Using the left click to select the first UPS and then left mouse click plus CTRL to select the last which should highlight all UPS.  Then Right Mouse click should pull up a tool tip.  

From that tool tip select 'Create Threshold - Other State Threshold'.  From the next window, you'll likely want to leverage the State radio button.  

 

Once you click next it will then give you a list of sensors, in the search box type 'UPS Operation Mode' and it will sort to all of the UPS Operation Mode sensors from all of the UPS you have selected.  In the lower left hand corner of this window you can use the 'Select all' checkbox to grab all the sensors at one.  Click next once you have selected the appropriate sensors.

From this next window it allows you to select the UPS Operation Mode which will create an alarm when matched.  For your use case above, I'd use 'On Battery'.  You can also set the severity, return to normal delay, and return to normal requires user input.  The severity allows you to determine what alarms actions are triggered depending on the notification policy selected in the final window.  

 

In the notification policy if you are using email, it should by default give you a 'Return to normal' email unless that option has been de-selected.  You can check this by diving into the Alert Actions in the Notification policy you are using.  


These types of alarms can be set against any sensors monitored in Data Center Expert.  you could also consider using State Mismatch and just have it notify you if the state is ever anything other than online.  If you have any issues, you can reach out to our technical support team at 877-908-2688 and they can step you through it (requires an active support contract).  Additionally, we do offer Administrator Training for Data Center Expert which is a full eight hour onsite training and covers all of this and more.  Hope this helps

 

(CID:151061517)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:11 PM
0 Likes
0
193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:11 PM

Re: how do I create an alarm to show the ups has no input power

This comment was originally posted on DCIM Support by Ric Turner on 2019-10-30


Hi Jonathon,

Thanks for very detailed reply.  I've actually gone through most of the steps you included, but once I get to the "Select Other State Sensors", my system displays 624 sensors, but it doesn't include any sensors for "UPS Operation".  I do however see a sensor for "On Battery"...do you think this would work?  It may work for one state (UPS switches to battery) but I'm not sure it would suffice for the "off battery" state.  

Seems as if a threshold for input voltage would also work.  It could send an alarm if if the input voltage drops below a certain value (10-20V perhaps?) and then one for Return to Normal.  

Your thoughts?

(CID:151063704)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:11 PM
0 Likes
0
193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:11 PM

Re: how do I create an alarm to show the ups has no input power

This comment was originally posted on DCIM Support by Jonathan Gould on 2019-11-01


Yes Ric, for the Model of this UPS 'On Battery' would be the best option.  You are correct that a threshold on voltage would also capture the same info.  

(CID:151063702)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:11 PM
0 Likes
0
193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:11 PM

Re: how do I create an alarm to show the ups has no input power

This comment was originally posted on DCIM Support by spezialist on 2019-11-03


Dear Ric Turner,

From your question:

...We can see where a Schneider technician added a "state" sensor for our Galaxy 4000 for "On Battery", but we can't figure out how to do this for all our other UPS devices.

If all other UPS devices are =SE= UPS's with SNMP cards, then you do not need to create any additional thresholds. After all, as soon as such a UPS switches to battery, it sends the SNMP trap to the DCE-server and you receive an critical alert about it. A similar situation occurs when the UPS switches back to main from the battery.

Does it not work for you like that?

With respect.

(CID:151062268)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 11:11 PM
0 Likes
0
193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 11:11 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
23
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric