Hello
The temperature sensors are associated to each cabinet and it is observed that the exhaust temperature shown in the dco is not the same as that shown in the dce.
Please could you help me with this topic.
Regards
Caroll
(CID:131962099)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:47 PM . Last Modified: 2 weeks ago
Hi Caroll,
The exhaust temperature is the temperature of the air exhausted by a rack. This is a calculated data displayed in Cooling overlay tooltip. Your associated temperature sensors are being displayed in the rack view, as well as in the 3D view (Measured plane).
Kind regards
(CID:131962332)