This question was originally posted on DCIM Support by dan peterman on 2020-01-08
hi,
i was looking to add threshold alerts, but didn't want to add them individually to each device. is there a way we can create a threshold alert that blankets all devices within DCE? or do i have to go through individually to each device and set it up?
thanks, Dan
(CID:153552254)
This answer was originally posted on DCIM Support by spezialist on 2020-01-08
Dear dan peterman,
Just select the required device group in the Alarm Configuration menu and select Create Thresholds in the context menu, for example:
Hope this helps you.
With respect.
(CID:153552259)
This comment was originally posted on DCIM Support by dan peterman on 2020-01-08
yes that does work, thanks for that!
what we are running into is that i didn't realize that some of our sites have different models and equipment so when i go to set a threshold it only returns equipment that has that specific sensor or category. so when i have 91 devices and i created a threshold but it only created it for 40 devices that was the reason why. but this does help! thanks!
(CID:153552299)
This comment was originally posted on DCIM Support by spezialist on 2020-01-08
Ok, very thanks for the good feedback :-).
(CID:153552316)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.