This question was originally posted on DCIM Support by Raul Velasquez Achury on 2019-08-15
buenas tardes, me pueden informar como realizo esta configuración en DCO, quedo atento a sus comentarios, gracias.
(CID:147784991)
This answer was originally posted on DCIM Support by Jef Faridi on 2019-08-16
Hi Raul,
Modelling parallel UPSs (in DCO) are unfortunately not directly supported, as sort of work around you might want to create a single UPS (with the combined capacity of the two UPSs) and set the Internal redundancy on the UPS to N+1.
In order to get the associations from DCE to work, you might want to create another UPS object with zero capacity (without power cabling) and place it next to the "main" UPS in DCO. In that way, you get a UPS model where you can associate DCE alarms.
Kind regards
(CID:147785100)