Hello Mark,
To better understand lost communication first I would to explain how a device can show lost communication in DCE. DCE using SNMP or ModBus to poll information from the device. During this polling period, if DCE doesn't receive replies via one those communication protocols the device goes into "lost communication". DCE will use this method exclusively to determine communication status. When it comes to troubleshooting here are the general guidelines to why DCE may lose communication to any given device
I would first check community string to confirm that DCE has to correct ones. Beyond that I would recommend that a packet capture to determine the root cause. To be more specific, two packet capture one closest to each end point DCE and the device.
Thank You
(CID:113641409)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:23 PM . Last Modified: 2023-10-22 04:27 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.