Talking about wireless sensor I´d like to know what is the name or identifier over the MIB to get the RSSI variable
(CID:140713349)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:56 PM . Last Modified: 3 weeks ago
Hi Victor.
You didn't mention which appliance you are using so I've provided for both the 250 as well as for the devices such as the 570.
If you're using a Netbotz appliance such as the 570, you can download the mib on the web page of the appliance:
http://
It's not a straight "What OID is for the value for this sensor"? I suggest to get a clearer picture here that you give specific names to these values. For this test, I've renamed the RSSI to "RSSI (sensor73AA)". This way we know exactly what value is associated with this sensor(it's last 4 of the mac address) instead of potentially having 20 +/- sensors all labeled RSSI.
Please note in this case the value is 83.
If you then poll iso.org.dod.internet.private.enterprises.netBotzAPC.netBotz.netBotzSensors.netBotzNumericSensors.otherNumericSensorTable.otherNumericSensorEntry.otherNumericSensorLabel
.1.3.6.1.4.1.5528.100.4.1.10.1.4
You get a list of all the sensors of this type (and others)
Please note that the highlighted sensor has an instance of 2810708973 and it is connected to the label "RSSI (sensor73AA)". To get any further info on this sensor, you poll other OIDs and look to match this SNMP instance. If I then poll:
.iso.org.dod.internet.private.enterprises.netBotzAPC.netBotz.netBotzSensors.netBotzNumericSensors.otherNumericSensorTable.otherNumericSensorEntry.otherNumericSensorValueInt
.1.3.6.1.4.1.5528.100.4.1.10.1.8
I get the following values. Please note that the instance of 2810708973 that matches the previous label "RSSI (sensor73AA)" is responding with the integer "83":
This is the RSSI for "RSSI (sensor73AA)" or wireless temp sensor Sensor Pod 100 T (00C0B700008273AA)
Sorry it's not easier but it was done this way due to the dynamic nature of the NetBotz appliance.
********************************************************************************************************************
********************************************************************************************************************
If you're using a NetBotz 250, it's much easier. You'll want to download the powernet.mib at www.apc.com/tools/download
You'll want to poll:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.environmentalMonitor.envWireless.wirelessSensorStatus.wirelessSensorStatusTable.wirelessSensorStatusEntry.wirelessSensorStatusRssi
.1.3.6.1.4.1.318.1.1.10.5.1.1.1.19
You may need the specific instance if you're trying to poll an individual sensor..
The rest of the wireless OIDs for the 250 can be found under:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.environmentalMonitor.envWireless
.1.3.6.1.4.1.318.1.1.10.5
Thanks,
Steve
(CID:140713649)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:56 PM . Last Modified: 3 weeks ago
Hi Victor.
You didn't mention which appliance you are using so I've provided for both the 250 as well as for the devices such as the 570.
If you're using a Netbotz appliance such as the 570, you can download the mib on the web page of the appliance:
http://
It's not a straight "What OID is for the value for this sensor"? I suggest to get a clearer picture here that you give specific names to these values. For this test, I've renamed the RSSI to "RSSI (sensor73AA)". This way we know exactly what value is associated with this sensor(it's last 4 of the mac address) instead of potentially having 20 +/- sensors all labeled RSSI.
Please note in this case the value is 83.
If you then poll iso.org.dod.internet.private.enterprises.netBotzAPC.netBotz.netBotzSensors.netBotzNumericSensors.otherNumericSensorTable.otherNumericSensorEntry.otherNumericSensorLabel
.1.3.6.1.4.1.5528.100.4.1.10.1.4
You get a list of all the sensors of this type (and others)
Please note that the highlighted sensor has an instance of 2810708973 and it is connected to the label "RSSI (sensor73AA)". To get any further info on this sensor, you poll other OIDs and look to match this SNMP instance. If I then poll:
.iso.org.dod.internet.private.enterprises.netBotzAPC.netBotz.netBotzSensors.netBotzNumericSensors.otherNumericSensorTable.otherNumericSensorEntry.otherNumericSensorValueInt
.1.3.6.1.4.1.5528.100.4.1.10.1.8
I get the following values. Please note that the instance of 2810708973 that matches the previous label "RSSI (sensor73AA)" is responding with the integer "83":
This is the RSSI for "RSSI (sensor73AA)" or wireless temp sensor Sensor Pod 100 T (00C0B700008273AA)
Sorry it's not easier but it was done this way due to the dynamic nature of the NetBotz appliance.
********************************************************************************************************************
********************************************************************************************************************
If you're using a NetBotz 250, it's much easier. You'll want to download the powernet.mib at www.apc.com/tools/download
You'll want to poll:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.environmentalMonitor.envWireless.wirelessSensorStatus.wirelessSensorStatusTable.wirelessSensorStatusEntry.wirelessSensorStatusRssi
.1.3.6.1.4.1.318.1.1.10.5.1.1.1.19
You may need the specific instance if you're trying to poll an individual sensor..
The rest of the wireless OIDs for the 250 can be found under:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.environmentalMonitor.envWireless
.1.3.6.1.4.1.318.1.1.10.5
Thanks,
Steve
(CID:140713649)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:56 PM . Last Modified: 2023-10-22 04:23 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.