This question was originally posted on DCIM Support by Thabo Maepa on 2018-08-31
Hi Team,
I've recently encountered an issue, i want to map temperature(wireless sensors) values on DCO, i did the association as desired.
As you can see the association is done:
Association showing to be okay
My 3D model doesnt map out the measured values. what might be the cause of this?
Please assist
Regards
Thabo
(CID:134025172)
Solved! Go to Solution.
This answer was originally posted on DCIM Support by Jef Faridi on 2018-08-31
Hi Thabo,
As illustrated, perhaps your cooling plan is on "Nothing" or "Calculated plan":
Temperature sensors should appear when/if we switch to "Measured plan":
Kind regards
(CID:134025208)
This answer was originally posted on DCIM Support by Jef Faridi on 2018-08-31
Hi Thabo,
As illustrated, perhaps your cooling plan is on "Nothing" or "Calculated plan":
Temperature sensors should appear when/if we switch to "Measured plan":
Kind regards
(CID:134025208)
This comment was originally posted on DCIM Support by Thabo Maepa on 2018-09-03
Hi Jef,
That is not the case, think it might have to do with the firmware of the sensors
(CID:134025487)
This comment was originally posted on DCIM Support by Jef Faridi on 2018-09-03
Hi Thabo,
But according your 2D screen-shoot, it seems the temperature sensor data is being displayed in DCO.
Kind regards
(CID:134025530)
This comment was originally posted on DCIM Support by Thabo Maepa on 2018-09-04
Hi Jef,
The sensors are there on the 2D model, but on the 3D nothing shows up.
Note: I'm Using a Netbotz 250
(CID:134026285)
This comment was originally posted on DCIM Support by Jef Faridi on 2018-09-05
Hi Thabo,
I've been running several tests since yesterday without any problem, wondering if it is possible to ask for a copy of your backup file so I can test it locally? I will send you an invite to my =S= box, so the data safely can be shared with me (if you would), thanks.
Kind regards
(CID:134026948)
This comment was originally posted on DCIM Support by Thabo Maepa on 2018-09-14
Hi I finally found my mistake, i discovered the Netbotz 250 as instead of SNMP. 😀
(CID:134032141)
This comment was originally posted on DCIM Support by Jef Faridi on 2018-09-15
Hi Thabo,
Great!, many thanks for the update.
Kind regards
(CID:134032365)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.