Will DCO 8.1 install in the following hardware:
HPE ProLiant DL360 Gen10 4114 85W 1P 16G-2R P408i-a 8SFF Base Server
(CID:125213394)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:01 AM . Last Modified: 2 weeks ago
Hi John MacDonald,
According to the information on page System requirements, we have:
Recommended StruxureWare Data Center Operation server configuration Server requirement guidelines (minimum)
- CPU: 4 cores minimum. We recommend 8 cores
- Memory: 16 GB RAM (absolute minimum requirement)
- 100 GB storage, speed minimum 170 MB/s
- Cluster network: 1 Gbps connection between nodes
- Disaster recovery network: 10 Mbps with low latency <100 ms
If your'e installing DCO on an existing server, note that DCO claims almost all memory (JVM about 8 GB and Postgres about 6 GB alone). Therefore, you may experience issues if you have other applications running on the server, such as surveillance and monitoring agents.
Server requirement guidelines for 10,000 racks across 200 rooms with 30 concurrent usersServer requirement guidelines for 20,000 racks across 400 rooms with 30 concurrent users
- 8 CPU cores
- 32 GB RAM
- 1 Gbps network connection between cluster nodes
- 100 GB storage, speed minimum 170 MB/s
- 16 CPU cores
- 64 GB RAM
- 1 Gbps network connection between cluster nodes
- 100 GB storage, speed minimum 170 MB/s
Thus, your physical server is no problem with DCO configuration up to 10,000 racks (which probably exceeds your real needs).
With respect.
(CID:125213407)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:01 AM . Last Modified: 2 weeks ago
Hi John MacDonald,
According to the information on page System requirements, we have:
Recommended StruxureWare Data Center Operation server configuration Server requirement guidelines (minimum)
- CPU: 4 cores minimum. We recommend 8 cores
- Memory: 16 GB RAM (absolute minimum requirement)
- 100 GB storage, speed minimum 170 MB/s
- Cluster network: 1 Gbps connection between nodes
- Disaster recovery network: 10 Mbps with low latency <100 ms
If your'e installing DCO on an existing server, note that DCO claims almost all memory (JVM about 8 GB and Postgres about 6 GB alone). Therefore, you may experience issues if you have other applications running on the server, such as surveillance and monitoring agents.
Server requirement guidelines for 10,000 racks across 200 rooms with 30 concurrent usersServer requirement guidelines for 20,000 racks across 400 rooms with 30 concurrent users
- 8 CPU cores
- 32 GB RAM
- 1 Gbps network connection between cluster nodes
- 100 GB storage, speed minimum 170 MB/s
- 16 CPU cores
- 64 GB RAM
- 1 Gbps network connection between cluster nodes
- 100 GB storage, speed minimum 170 MB/s
Thus, your physical server is no problem with DCO configuration up to 10,000 racks (which probably exceeds your real needs).
With respect.
(CID:125213407)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:01 AM . Last Modified: 2 weeks ago
Thanks for your comments but I was asking due to the RAID controller - please confirm DCO 8.1 will install on this device, thanks!
(CID:125213425)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:01 AM . Last Modified: 2 weeks ago
Hi John MacDonald,
In your question, you did not ask about the RAID controller 😀.
And yet, according to the official specification for the HPE Smart Array P408i-a Controller on page HPE Smart Array P408i-a Controller - Overview, its guaranteed support for CentOS Linux (see also file HPE Smart Array Operating System Support Matrix). Let me remind you that DCO-8.1 is based on CentOS-7 Linux.
With respect.
(CID:126158687)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:02 AM . Last Modified: 2 weeks ago
Hi John MacDonald,
Have you solved your problem or not?
With respect.
(CID:126159012)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:02 AM . Last Modified: 2023-10-22 04:22 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.