Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Which is the best way to monitor 4-20mA sensors in DCE
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49690members
Join Now
243141posts
Join Now

Which is the best way to monitor 4-20mA sensors in DCE

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
GaborNovak
Ensign GaborNovak
Ensign
‎2020-08-10 04:13 AM
0 Likes
13
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-10 04:13 AM

Which is the best way to monitor 4-20mA sensors in DCE

I would like to monitor 40 temperature sensors, the sensors will measure chiller liquid temperature.

NetBotz systems doesn’t support this amount of 4-20mA sensors. The NBPD0129 is not supported, this product is discontinued.

 

Which method is the best way to do that?

Labels
  • Data Center Expert
Tags (1)
  • Tags:
  • 4-20ma
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
13 Replies 13
APC_Steve
Lt. Commander APC_Steve Lt. Commander
Lt. Commander
‎2020-08-10 05:08 AM
0 Likes
12
1293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-10 05:08 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

Hi @GaborNovak ,

 

If you can still find the NBPD0129, it is supported on the version 3 appliances that support USB such as the 570. Other than that, you've obviously noticed that there aren't enough connections on the 750. You'd really need a lot of them to support what you need. In any case, those connections on the units or the pods are the only way NetBotz can support 4-20 sensors. NetBotz in turn is the only APC supported platform to monitor 4-20 and get them into DCE.

 

I know of no 3rd party options but that's what you'd have to look for. DCE can only support SNMP and Modbus devices but I know of none that would offer this option.

 

Thanks,

Steve

Tags (1)
  • Tags:
  • english
Share
Reply
GaborNovak
Ensign GaborNovak
Ensign
‎2020-08-10 06:25 AM
0 Likes
11
1284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-10 06:25 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

@APC_Steve 

 

The 3rd party option can be a solution. I know such a device which can read 4-20mA sensors and has RS485 modbus output, the problem that it cannot convert the current readings to physical readings.

 

I'm searching for some device which can do this task. Reads 4-20mA sensors, convert the measured current reading to temperature and has a RS485 output.

Tags (1)
  • Tags:
  • english
Share
Reply
Shaun
Ensign Shaun Ensign
Ensign
‎2020-08-10 06:53 AM
0 Likes
10
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-10 06:53 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

Hi,

 

We may be able to handle the conversion on the DCE, depending on the sensor.  The DCE will require a DDF (Device Definition) for a third-party modbus device anyway, eg to instruct the DCE which registers the value lives in.

 

Most 4-20mA temperature sensors use a linear scale  (eg, for a 0-100C sensor, every 6.25C is 1mA), which is well within the capabilities of the DDF when translating modbus values back to real data.  (I regret I'm too mathematically challenged to promise the same for logarithmic sensors.)

Tags (1)
  • Tags:
  • english
Share
Reply
GaborNovak
Ensign GaborNovak
Ensign
‎2020-08-10 08:45 AM
0 Likes
9
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-10 08:45 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

Hi @Shaun

 

On site there is no measurement the customer wants us to build this system and monitor the readings via DCE system. We can use for example PT100 sensors.

 

If I’m correct the DCE doesn’t has scaling function. So it cannot convert the current reading to physical value. Is this correct?  I haven’t seen such DDF which was capable to do this conversion.

 

For example: When we use MODBUS we read the modbus address the return value is our measurement. In the DDF file we can define the sensor type, sensor label, decimal value, sensor increment, etc.

 

So how to convert in the DDF xml file this current value to temperature value?

Tags (1)
  • Tags:
  • english
Share
Reply
APC_Steve
Lt. Commander APC_Steve Lt. Commander
Lt. Commander
‎2020-08-10 08:54 AM
0 Likes
8
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-10 08:54 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

Hi @GaborNovak ,

 

The option @Shaun had mentioned can work. No, DCE has no scaling option available to the user but a DDF specifically designed for this sensor / modbus output combination can handle any scaling, multiplication, etc that would be needed. Each sensor could be converted by the DDF to output data based on the return of the different registers. For instance if 4 mA = 0 degrees and 20 mA = 100 degrees, that should be a relatively simple calculation. 

 

Steve

Tags (1)
  • Tags:
  • english
Share
Reply
ATrabert
Ensign ATrabert Ensign
Ensign
‎2020-08-10 09:11 AM
1 Like
1
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-10 09:11 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

I agree with Shaun and Steve that the ddf could do this type of scaling as long as it is linear.  However I don't think it's the best solution suited for it. 

 

Instead you would use a type of IO gateway that reads the 4-20 ma sensor, scales it and converts it into modbus tcp.  Then all the ddf does is read the raw value. 

 

I would recommend engaging the buildings team, but you should be able to use SmartX AS-P controller and IO modules to do this.  https://ecostruxure-building-help.se.com/bms/topics/show.castle?id=10758&locale=en-US&productversion...

Tags (1)
  • Tags:
  • english
Share
Reply
DavidChild
Admiral DavidChild Admiral
Admiral
‎2020-08-11 01:57 AM
0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-11 01:57 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

Hi,

 

You can use the EcoStruxures Building Operation's AS-P with the relevant UI modules. Read in the 4-20mA signal into the UI module

 

Then the temperature reading C of F can be re-transmitted onwards using the AS-P as a slave or server as a BACnet IP/MSTP or modbus TCP/RS485 device.

Tags (1)
  • Tags:
  • english
Share
Reply
GaborNovak
Ensign GaborNovak
Ensign
‎2020-08-12 12:05 AM
0 Likes
5
1219
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-12 12:05 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

Hi @APC_Steve 

 

This kind of DDF will be created by the DDF team? Which information must I provide them to make this kind of special DDF? I would like to test this version to before I make it available for the customer. It is useful to see how it works in real life.

I have an Advantech controller which can read the 4-20mA signal and transfer the current readings over TCPIP modbus communication to the DCE server.

Tags (1)
  • Tags:
  • english
Share
Reply
APC_Steve
Lt. Commander APC_Steve Lt. Commander
Lt. Commander
‎2020-08-12 06:11 AM
0 Likes
4
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-12 06:11 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

Hi @GaborNovak ,

 

You'd need to provide them the register map for the sensors you'd want and detail on the sensors, maybe the manual that describes what values in the 4-20 range are equal to what real-life values. Potentially even link this forum post .

 

Go to https://ddf.ecostruxureit.com/

it just keeps allowing you to scroll but if you search for something (find it or not) the short list will also end with a link for 

Don't see the DDF you are looking for?Submit a request.
I'd copy that link but I'm not sure if it's specific to the browsing instance.
 
I had already let them know you might be coming.
 
Steve
Tags (1)
  • Tags:
  • english
Share
Reply
ATrabert
Ensign ATrabert Ensign
Ensign
‎2020-08-12 07:25 AM
0 Likes
3
1197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-12 07:25 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

@GaborNovak you would also need to purchase an asset definition service https://helpcenter.ecostruxureit.com/hc/en-us/articles/360008128678-Asset-Definition-service-for-DDF... in order for the ddf to be created regardless if the monitoring device scales the value or if the value is scaled in the ddf.

Tags (1)
  • Tags:
  • english
Share
Reply
APC_Steve
Lt. Commander APC_Steve Lt. Commander
Lt. Commander
‎2020-08-12 07:51 AM
0 Likes
2
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-12 07:51 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

That is quite likely but if they have support contracts, they may get to work out a deal before the end of the year.

Tags (1)
  • Tags:
  • english
Share
Reply
GaborNovak
Ensign GaborNovak
Ensign
‎2020-08-12 09:31 AM
0 Likes
1
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-12 09:31 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

Requesting new DDF was for free if I remember correctly. Has this option changed?

 


Our Data Center Expert DDF repository contains the most commonly requested DDFs. New 3rd party DDFs for DCE can only be added through the Asset Definition service. 


Regarding to the article, the free DDF creation is over. I'm right?

 

I haven’t find the asset definition service in my price list. Could you send an APC Part Number?

 

We have support contract for the DCE servers and for the nodes. (StruxureWare Data Center Expert Basic Software Support Contract)

I read that in the description that the asset definition service covers 20 DDF creation and 3 modification request to each DDF.

 


Your DDFs will be delivered on a pre-defined date. Pricing is customized based on the number of DDFs you request. 


So, it’s a bit confusing for me. Where will I become the information about the delivered date and the pricing, etc.  Maybe after the DDF request process via email?

 



 

Tags (1)
  • Tags:
  • english
Share
Reply
APC_Steve
Lt. Commander APC_Steve Lt. Commander
Lt. Commander
‎2020-08-12 09:56 AM
1 Like
0
1176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-12 09:56 AM

Re: Which is the best way to monitor 4-20mA sensors in DCE

Hi @GaborNovak ,

 

I spoke to someone responsible for DDF creation. He stated:

We are doing an interim solution regards DDF credits. The customer must have the following:

 

  • Purchased the support contract before May 20th 2020
  • Provide Serial and MAC of the server and screen shot of their license key page
  • Support contract must match the installed license key count

 

If these are met then we will assign DDF credits free of charge that they can use between now and the end of the current contract.

 

The skus for the service are as follows

 

WNSWACS1DDF

WNSWACS5DDF

WNSWACS10DDF

WNSWACS20DDF

 

The DDF under this service will be delivered within 20 business days and will also include up to 3 revisions.

 

Thanks,

Steve

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric