  • Users are not working after DCO upgrade to version 8.3
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49516members
Join Now
242865posts
Join Now

Users are not working after DCO upgrade to version 8.3

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:03 PM
0 Likes
9
187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:03 PM

Users are not working after DCO upgrade to version 8.3

This question was originally posted on DCIM Support by Andres Cordero on 2019-05-03


Hello Support,
We performed the DCO upgrade from 8.2 to version 8.3 using the link below as guide:

https://sxwhelpcenter.ecostruxureit.com/display/public/UADCO8x/Getting+from+previous+versions+to+DCO... 

The upgrade logs shows the process as successful (Attached file "upgrade logs")
The about section shows the version correctly. (Attached file "upgrade completed")

Also, the webmin seems to be working normal.

The problem is with the User authentication.
The service is not working at all. So, we can't get access to the platform.
Local Users and AD User are useless. (Attached file "error users").


upgrade logs.txt

(CID:143755215)

Labels
  • Data Center Operation
Share
  • All forum topics
  • Previous Topic
  • Next Topic
9 Replies 9
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:03 PM
0 Likes
0
187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:03 PM

Re: Users are not working after DCO upgrade to version 8.3

This comment was originally posted on DCIM Support by Greg Sterling on 2019-05-03


Can you also attach the server.log file from the dco server?

Also, does webmin show the DCO application and database services are all running?

How much time since the upgrade completed has passed since the server rebooted?

You're upgrading from DCO 8.2.2 to 8.3, there are a few database schema update which have to be applied before the dco server upgrade is completed. These updates can take some time to complete.

Regards

Greg Sterling

(CID:143755222)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:03 PM
0 Likes
0
187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:03 PM

Re: Users are not working after DCO upgrade to version 8.3

This comment was originally posted on DCIM Support by Andres Cordero on 2019-05-04


Hello Greg,

  1. I will to schedule with our customer to try again the upgrade on next monday.
    Please confirm the path to download the server.log file.
  2. Yes, Please check attached file. (status)
  3. 20 minutes, more or less.

 

(CID:143755231)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:03 PM
0 Likes
0
187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:03 PM

Re: Users are not working after DCO upgrade to version 8.3

This comment was originally posted on DCIM Support by Greg Sterling on 2019-05-04


I dont think I would rerun the upgrade, it looked like it worked based on the log file you had attached.

Can you upload the server.log file so we can see if there were errors in the DCO services when they restarted? The server log can be found in this folder on the dco server /opt/jboss-as/standalone/log

Regards

Greg Sterling

(CID:143755236)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:03 PM
0 Likes
0
187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:03 PM

Re: Users are not working after DCO upgrade to version 8.3

This comment was originally posted on DCIM Support by Andres Cordero on 2019-05-04


Greg,

This server is in production.

That's why before run the upgrade we created a snapshot,  to have a restore point.

So after the upgrade and seeing that the server was not working as expected. We restored the VM to the snapshot point.

Currently the server is on version 8.2.
We must re-run the upgrade in order to extract the requested file.

By the way, we ran the upgrade process 3 times and we had the same result.

(CID:143755239)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:03 PM
0 Likes
3
187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:03 PM

Re: Users are not working after DCO upgrade to version 8.3

This answer was originally posted on DCIM Support by Lukas Jegerlehner on 2019-07-26


Hi all. I have the exact same issue. 

the field "force_single_sign_on" is missing in the table public.users. --> no user can login. 

I m wondering if you got the issue solved and how?

 

The upgrade went well. I am suspecting an issue after rebooting within the java which should adjust the database. somehow it did not happen. 

 

Br Lukas

 

 

(CID:147198830)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:04 PM
0 Likes
0
187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:04 PM

Re: Users are not working after DCO upgrade to version 8.3

This comment was originally posted on DCIM Support by Greg Sterling on 2019-07-26


I'm waiting on dev help for the other reported problem (perhaps you logged that call?)

Regards

Greg Sterling

(CID:147198880)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:04 PM
0 Likes
0
187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:04 PM

Re: Users are not working after DCO upgrade to version 8.3

This comment was originally posted on DCIM Support by Lukas Jegerlehner on 2019-07-28


Hi Greg, what was the other reported problem?

Could it have anything to do with custom property fields  ....

I hope the waiting doesn't take too long 😉

Cheers Lukas

(CID:147199338)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:04 PM
0 Likes
0
187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:04 PM

Re: Users are not working after DCO upgrade to version 8.3

This comment was originally posted on DCIM Support by Lukas Jegerlehner on 2019-08-05


please see my findings below:
here is a quick description how to provoke the case. Can you and your development team please look into fixing the issue for the next release. Thank you in advance.
  1. Two clean dco installations (version 8.2.12)

  2. Connect DR node.
  3. For dco2 the ISXO_BACKUP_SITE field, within the /etc/isx-operations/config file, will become 1 (slave).
  4. promote dco2 —> ISXO_BACKUP_SITE for dco2 will become 2 (master)
  5. upgrade dco2 to the latest version 8.3.2. Schema will not update due to ISXO_BACKUP_SITE = 2 (wasn’t cleared).  
  6. ExecStartPre=/usr/libexec/dco-platform/schemaUpgrade.sh —> The IF within the schemaUpgrade Shell checks if the field ISXO_BACKUP_SITE is empty.  
  7. In the case of switching the DR back and forth between two servers (this could happen over time), both servers will end up with a field entry ISXO_BACKUP_SITE = 2, once disconnected again. 
  8. —> solution: check the IF statement within schemaUpgrade.sh, which was added after version 8.2.12. For the slave ISXO_BACKUP_SITE = 1 it makes sense to not run a schema update. For 2 and ‘ ‘ schema upgrades may should be performed ?

(CID:147201855)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 07:04 PM
0 Likes
0
187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 07:04 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric