  • Re: Upgrade LINUX OS and install new security files in DCE and DCO
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51004members
Join Now
245054posts
Join Now

Upgrade LINUX OS and install new security files in DCE and DCO

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:50 PM
0 Likes
5
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:50 PM

Upgrade LINUX OS and install new security files in DCE and DCO

This question was originally posted on DCIM Support by Luis Lopez Borbon on 2018-08-17


Hello Support team,

I want to know if the upgrade files in DCE and DCO also update the LINUX OS cyber security threats? If not, how is the way to update the OS or install the security files in both servers DCE and DCO… if the LINUX OS is updated, is possible having issues when the client is opened? do you have some steps to update the cyber security files in DCE and DCO?

regards

(CID:133372628)

Solved! Go to Solution.

Labels
  • Data Center Expert
  • Data Center Operation
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:50 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:50 PM

Re: Upgrade LINUX OS and install new security files in DCE and DCO

This answer was originally posted on DCIM Support by Justine Chester on 2018-08-17


Hi Luis,

Good day!

The security fixes for DCE and DCO's operating systems are included with the update files that we share with the customers. The list of security fixes and vulnerabilities are available from the links below:

 

  • DCE

 

  • DCO

By knowing which vulnerabilities are identified and addressed on each software version, we can convince our customers to update their software (which will require a valid and updated software support contract).

Instructions for the DCE and DCO update are available from the following links:

 

  • DCE Update Instructions

 

  • DCO Update Instructions

 

I hope this answers your question.

 

Kind regards,

 

Justine Chester

(CID:133372644)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:50 PM
0 Likes
0
141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:50 PM

Re: Upgrade LINUX OS and install new security files in DCE and DCO

This answer was originally posted on DCIM Support by Justine Chester on 2018-08-17


Hi Luis,

Good day!

The security fixes for DCE and DCO's operating systems are included with the update files that we share with the customers. The list of security fixes and vulnerabilities are available from the links below:

 

  • DCE

 

  • DCO

By knowing which vulnerabilities are identified and addressed on each software version, we can convince our customers to update their software (which will require a valid and updated software support contract).

Instructions for the DCE and DCO update are available from the following links:

 

  • DCE Update Instructions

 

  • DCO Update Instructions

 

I hope this answers your question.

 

Kind regards,

 

Justine Chester

(CID:133372644)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:50 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:50 PM

Re: Upgrade LINUX OS and install new security files in DCE and DCO

This comment was originally posted on DCIM Support by spezialist on 2018-09-04


Dear Luis Lopez Borbon,

Tell us, please, have you solved this question or not?

With respect.

(CID:134026504)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:50 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:50 PM

Re: Upgrade LINUX OS and install new security files in DCE and DCO

This comment was originally posted on DCIM Support by Luis Lopez Borbon on 2018-09-05


Hello Team ,

according the answer by Justine Chester, I explained to my customer that all security fixes are includes inside the upgrade file. I did the upgrade in each server DCE – DCO following the normal upgrade instructions. 

Thank you for your help.

(CID:134026856)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:50 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:50 PM

Re: Upgrade LINUX OS and install new security files in DCE and DCO

This comment was originally posted on DCIM Support by Justine Chester on 2018-09-05


Hi Luis,

 

Would you be able to accept the answer that I shared by upvoting it?

Thanks 😀

 

Kind regards,

 

Justine Chester

(CID:134026862)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 09:51 PM
0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 09:51 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
23
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric