  • Unstable communicatiom with pCOWeb
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49531members
Join Now
242879posts
Join Now

Unstable communicatiom with pCOWeb

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 06:35 PM
0 Likes
8
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 06:35 PM

Unstable communicatiom with pCOWeb

This question was originally posted on DCIM Support by Valentin Kozlov on 2017-08-01


Hi guys!

I have two Leonardo downflow CRAC units with pCOWeb installed.

Both demonstrate very unstable communication via SNMP, Modbus TCP and Web. It allow to log in to the web interface but when I click some tab, the web card have no response and browser show timeout error. And after some time (2-5 min) it back to live again. Sometimes I even can not log in, but sometimes it works fine for a short time and I can log in and switch between tabs, but in 5 - 7 minutes I'll lost communication again.

The issue is similar on both units.

Can anyone advice how to troubleshoot it?

 

Here is communication status graph from DCE:

(CID:123343223)

Solved! Go to Solution.

Labels
  • Data Center Expert
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 06:36 PM
0 Likes
0
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 06:36 PM

Re: Unstable communicatiom with pCOWeb

This answer was originally posted on DCIM Support by Valentin Kozlov on 2017-08-04


Hi All!

 

I fix my isue. The reason was in incorrect network settings on pCOWeb card.

It have 3 Eth subintarfaces and Eth0 was configured for DHCP and Eth1 was configured for static address.

Removing DHCP and setting static address for Eth0 resolve the issue.

(CID:123344308)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
8 Replies 8
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 06:35 PM
0 Likes
3
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 06:35 PM

Re: Unstable communicatiom with pCOWeb

This answer was originally posted on DCIM Support by Steven Marchetti on 2017-08-01


Hi Valentin,

 

If this is only happening to these 2 devices, it does sound like the devices themselves. Add to this the fact that you mention that " the web card have no response and browser show timeout error." it sounds like the card is either busy or the network is having issues. Looking at the communications graph is quite interesting too. The graph looks perfect...like the lost and regained comms happen at precisely regular intervals (likely due to polling frequency). 

 

Do you know if there's something else polling the devices? Have you looked at the logs for the devices? Are there other devices on the same subnet that works? If the devices is in a distant subnet, have you tried installing a VM and removing the device from this DCE and adding it to a DCE VM on that same subnet to rule out networking issues?


Steve

(CID:123343236)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 06:35 PM
0 Likes
0
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 06:35 PM

Re: Unstable communicatiom with pCOWeb

This comment was originally posted on DCIM Support by Valentin Kozlov on 2017-08-02


Hi Steve!

Devices directly connected to our APC switch and polled by DCE. Other devices on this subnet (UPS and PDUs) works fine, so probably it's a not network related issue.

I'll try to connect unit to VM directly, of course.

 

I have no wide experience with pCOWeb. Usually we are use Modbus RTU + gateway option and all works fine. This time customer order web cards, but I can't to add it to DCE by SNMP (DCE recognize it as Linux workstation). Thats why I need to use Modbus TCP.

 

(CID:123343358)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 06:35 PM
0 Likes
0
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 06:35 PM

Re: Unstable communicatiom with pCOWeb

This comment was originally posted on DCIM Support by Miguel angel solans on 2017-08-02


pCOWEB can connect by SNMP and Modbus IP if you wish

(CID:123343600)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 06:36 PM
0 Likes
0
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 06:36 PM

Re: Unstable communicatiom with pCOWeb

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-08-02


Hi Valentin,

 

pCOWeb cards are weird when it comes to SNMP. They re-use OIDs. The same OID sued for your cooling unit for one sensor may be a totally different sensor on another system. Additionally, they often do not define themselves which is necessary when discovering via SNMP. If you have multiple pCOWeb devices, they will often just use the first pCOWeb based DDF  DCE finds for them. Modbus it often the best option.

Are there multiple slave addresses connected? If you have multiple slave addresses there could be an issue where there's too much issue on the bus. Similarly, if other systems are monitoring the device, that may interfere with DCE polling the device.

I'm also wondering if the way DCE is polling the device may have an effect on it. I have seen some instances (not pCOWeb specifically though) where we may poll individual registers and a device will work fine but if we poll a block of registers, the device doesn't respond well. 


Steve

(CID:123343606)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 06:36 PM
0 Likes
1
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 06:36 PM

Re: Unstable communicatiom with pCOWeb

This answer was originally posted on DCIM Support by Warren Robb on 2017-08-01


As another suggestion, it may be an idea to validate the network port that the card it plugged into on the switch.  Ask the network team to have a check on the duplex option and port speed.

(CID:123343260)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 06:36 PM
0 Likes
0
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 06:36 PM

Re: Unstable communicatiom with pCOWeb

This comment was originally posted on DCIM Support by Valentin Kozlov on 2017-08-02


Thanks Warren! I'll try to check this out.

(CID:123343359)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 06:36 PM
0 Likes
0
183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 06:36 PM

Re: Unstable communicatiom with pCOWeb

This answer was originally posted on DCIM Support by Valentin Kozlov on 2017-08-04


Hi All!

 

I fix my isue. The reason was in incorrect network settings on pCOWeb card.

It have 3 Eth subintarfaces and Eth0 was configured for DHCP and Eth1 was configured for static address.

Removing DHCP and setting static address for Eth0 resolve the issue.

(CID:123344308)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 06:36 PM
0 Likes
0
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 06:36 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric