This question was originally posted on DCIM Support by Javier Alejandro Pignata on 2019-09-12
Hi! I'm having estimated load values in measured PDUs even when the adjusted nameplate values were set to 0. Yesterday while working on this, the values were correct (no estimated values in measured PDUs), but today when I opened DCO, I found this issue.
I'd appreciate some elightenment.
(CID:148769482)
This answer was originally posted on DCIM Support by Greg Sterling on 2019-09-12
Hello Javier.
One quick question. In the tools menu, preferences, how is the "power capacity" item set in your DCO installation? Is it set to "predictive power" like below?
If yes, then the estimated load in racks with measured power will be based on the measured power values, not the derated nameplate values in the assets themselves.
If is set to adjusted nameplate, then we have to look elsewhere.
Regards
Greg Sterling
(CID:148769797)
This comment was originally posted on DCIM Support by Javier Alejandro Pignata on 2019-09-12
It is set in "Predicted Power"
Question: With this option, in racks where there is no posibillity of measurment, the load is taken from the adjusted nameplate too?
(CID:148769800)
This comment was originally posted on DCIM Support by Greg Sterling on 2019-09-12
Yes/Correct. If a rack does not have measurements, then the estimated load will be based on the standard nameplate or derated nameplate.
Regards
Greg Sterling
(CID:148769805)
This comment was originally posted on DCIM Support by Javier Alejandro Pignata on 2019-09-12
Thank you very much. It worked!
Kind regards
(CID:148769803)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!