Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Unable to change temperature value from F to Celsius
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49242members
Join Now
242456posts
Join Now

Unable to change temperature value from F to Celsius

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
Stefano
Crewman Stefano
Crewman
‎2020-11-11 06:35 PM
0 Likes
11
548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-11 06:35 PM

Unable to change temperature value from F to Celsius

Hi,

 

How do I change temperature sensor value to Degree Celsius in DCO. Currently it is showing Fahrenheit. The temp/humidity sensor is directly connected to RPDU.

 

I saw the topic below, but unfortunately changing the from US to Metric doesn't work for me.

https://community.exchange.se.com/t5/EcoStruxure-IT-forum/Temperature-value-setting/m-p/202199#M1593

 

Can you support me on this ?

 

Thank you

 

DCO_Temp.JPG

 

 

Labels
  • Data Center Operation
Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
11 Replies 11
Jef
Commander Jef Commander
Commander
‎2020-11-12 12:40 AM
2 Likes
9
539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-12 12:40 AM

Re: Unable to change temperature value from F to Celsius

Hi Stefano,

Additional to your illustrated settings (in desktop client, Tools > Preferences > General), measurement units in DCO (and ITA) are appearing according to the settings selected by the operation system on the client's computer. The 'Region' control panel allows user to select these settings:
Capture-jf.JPG

Kind regards,

Jef

Tags (1)
  • Tags:
  • english
Share
Reply
Stefano
Crewman Stefano
Crewman
‎2020-11-12 09:32 AM
0 Likes
8
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-12 09:32 AM

Re: Unable to change temperature value from F to Celsius

Hi Jef,

 

thank you so much for your suggestion, looks like the settings are the same (except some italian word), it's very strange

cause on the same workstation DCO shows F° and DCE C° 

 

 

DCO.png

 

os_sett.JPG

 

Best regards,

Stefano

Tags (1)
  • Tags:
  • english
Share
Reply
Jef
Commander Jef Commander
Commander
‎2020-11-13 04:49 AM
0 Likes
7
497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-13 04:49 AM

Re: Unable to change temperature value from F to Celsius

Hi Stefano,

You are most welcome & many thanks for the useful illustrations.
That's a different scenario. The units in the alarm description filed are independent of the desktop settings.
This is the way DCE reports alarms and alarm descriptions to DCO. DCO dose not translate the alarm descriptions and will display as they are. 

Kind regards,

Jef

Tags (1)
  • Tags:
  • english
Share
Reply
Stefano
Crewman Stefano
Crewman
‎2020-11-13 05:28 AM
0 Likes
6
492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-13 05:28 AM

Re: Unable to change temperature value from F to Celsius

Hi Jef,

 

ok thanks, should I change switch to METRIC on DCE server in order to see C° on DCO?

 

Regards

 

Stefano

Tags (1)
  • Tags:
  • english
Share
Reply
Jef
Commander Jef Commander
Commander
‎2020-11-13 05:42 AM
0 Likes
5
489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-13 05:42 AM

Re: Unable to change temperature value from F to Celsius

Hi Stefano,

Yes, you can try that.

Apparently your DCE server regional settings might be in US or something and you might want to change it to something like English (METRIC).
It can be done via DCE desktop client, System > Server Administration Settings > Time Settings , and then under "Regional Settings" change the Server Local to English (METRIC).

Then the Alarms notifications (reported from DCE) would be in Metric in DCO.

 

Kind regards,

Jef

Tags (1)
  • Tags:
  • english
Share
Reply
Stefano
Crewman Stefano
Crewman
‎2020-11-17 01:56 AM
0 Likes
4
456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-17 01:56 AM

Re: Unable to change temperature value from F to Celsius

Hi Jef,

 

great! I tried to set English METRIC but after the server restart the configuration didn't change ( tried 3 times ).

Could be a bug? I will try to upgrade DCE version from 7.7.1.40 to 7.8.0.47, probably it will solve it.

I will update you soon.

 

Regars

Stefano

Tags (1)
  • Tags:
  • english
Share
Reply
Stefano
Crewman Stefano
Crewman
‎2020-11-18 01:17 AM
0 Likes
3
450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-18 01:17 AM

Re: Unable to change temperature value from F to Celsius

Hi Crew,

 

I completed the DCE upgrade, but unfortunately the issue is still there.

 

I tried to change locale setting to English Metric or Italian couple of times but after the server restart, English US comes back into configuration menu.

 

Any suggestions?

 

Kind regards,

Stefano

 

 

Tags (1)
  • Tags:
  • english
Share
Reply
TechieBala
Ensign TechieBala Ensign
Ensign
‎2020-11-18 04:43 AM
1 Like
2
443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-18 04:43 AM

Re: Unable to change temperature value from F to Celsius

Hi @Stefano  I just realized that the issue which you want to resolve is on the DCO client for the alarms that are received from the DCE server not on the DCE desktop client itself. As per your screen shot, you are already able to see the DCE temperature unit in Celsius, but you are seeing the temperature alarms in Fahrenheit. Let me also investigate and I will let you know if I find something for you soon. Thanks!

 

Regards,

Bala

Tags (1)
  • Tags:
  • english
Share
Reply
Stefano
Crewman Stefano
Crewman
‎2020-11-18 06:19 AM
0 Likes
1
435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-18 06:19 AM

Re: Unable to change temperature value from F to Celsius

Hi Bala,

 

thank you so much!

Actually I am able to see C° as shown on the screen shot, because I changed the configuration from DCE client side.

File -> Client Preferences -> Client Language Settings -> Select Language -> English - Metric

 

Server side if I change the time settings in the System menu from US to Metric, after reboot the locale configuration show back US.

Please let me know if your suspicions are well founded... after the investigation on DCO client of course.

 

Regards,

 

Stefano

 

 

Tags (1)
  • Tags:
  • english
Share
Reply
TechieBala
Ensign TechieBala Ensign
Ensign
‎2020-11-22 06:38 AM
0 Likes
0
380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-22 06:38 AM

Re: Unable to change temperature value from F to Celsius

Hi @Stefano I am sorry for the delay. I was able to change the Server Locale to English Metric without an issue in DCE, and then I was able to receive the temperature alarms in Celsius on DCO as well. So It looks like that the issue which you are experiencing needs to be investigated in depth. I suggest you to contact our regional customer care team/FSR to analyze the issue further so that they can collect the required details to provide further recommendation. Thanks for your understanding! 

Tags (1)
  • Tags:
  • english
Share
Reply
Evans87
Evans87
Cadet
‎2020-11-25 03:38 AM
0 Likes
0
361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-25 03:38 AM

Re: Unable to change temperature value from F to Celsius

Yes, I got the same issues Target EHR

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric