We have two stand-alone DCE severs which are polling same devices. I noticed that sometimes the two servers got different data from the same device.
The device is a circuit breaker which communicates with DCE in MODBUS via a power meter gateway. Both servers monitor the breaker state. One server reports the breaker is in OPEN state while another server reports the breakers is in CLOSE state . I tried Request Device Scan and nothing changed.
I tried to deleted the device and add it again, the server then reported correct state.
(CID:149785687)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:48 PM . Last Modified: 2 weeks ago
Same DDF version Files on both Servers?
(CID:149785696)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:48 PM . Last Modified: 2 weeks ago
yes, same DDF version files on both servers.
(CID:149785701)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:49 PM . Last Modified: 2023-10-22 04:08 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.