This question was originally posted on DCIM Support by Paul O on 2019-12-20
Hi, I'm trying to get some Tripp Lite UPS to alarm to Struxureware. Struxureware discovers the UPS and I can view device sensors. I downloaded the most recent Tripp Lite UPS DDF (version 6) and TrippLite WEBCARDLX DDF (version 7). I go to Alarm Configuration and select a UPS and get "UPS - <ip address> contains no device alarms" (the ip address is correct). How do I tell Struxureware to use the DDF for this UPS? Struxureware version 7.2.2.76
(CID:153092111)
Solved! Go to Solution.
This answer was originally posted on DCIM Support by spezialist on 2019-12-20
Dear Paul O,
Since you are connecting 3rd party UPS to DCE software, first I highly recommend updating your UPS MIB DDF-file. You have a very old version of DCE-7.2.2 with an outdated version of UPS MIB v.4. The latest version of the UPS MIB v.11 DDF-file can be downloaded from the DDF resource, for example, like this:
Additionally, check again that you are using the correct and latest DDF-files for your Tripp Lite UPS.
In addition, I highly recommend that you take the time to upgrade your DCE software to the latest version of DCE-7.8.0. Since older versions of DCE software may no longer be supported when contacting to =SE= technical support.
In addition, you may find these two similar topics useful: and I am testing Tripp-Lite UPS unit compatibility with Struxureware software and found that Struxureware is not able to report any information, critical alarms from Tripp-Lite UPS unit in short or details email alert.
With respect.
(CID:153092328)
This comment was originally posted on DCIM Support by spezialist on 2019-12-20
Dear Paul O,
Can you show a couple of screenshots from DCE-client, please? And then they will help you faster and better 😀.
With respect.
(CID:153092162)
This answer was originally posted on DCIM Support by Paul O on 2019-12-20
Here is the DFF files we have on the server:
Here is a device running the older TrippLite websnmpcard:
Here is what we get on a device running the newer WEBCARDLX:
Mix of WEBCARDLX and websnmpcards and various Tripp-Lite models. WEBCARDLX version 15.5.2, websnmpcard version 12.06.0069.
Please let me know what other information might be helpful.
(CID:153092306)
This answer was originally posted on DCIM Support by spezialist on 2019-12-20
Dear Paul O,
Since you are connecting 3rd party UPS to DCE software, first I highly recommend updating your UPS MIB DDF-file. You have a very old version of DCE-7.2.2 with an outdated version of UPS MIB v.4. The latest version of the UPS MIB v.11 DDF-file can be downloaded from the DDF resource, for example, like this:
Additionally, check again that you are using the correct and latest DDF-files for your Tripp Lite UPS.
In addition, I highly recommend that you take the time to upgrade your DCE software to the latest version of DCE-7.8.0. Since older versions of DCE software may no longer be supported when contacting to =SE= technical support.
In addition, you may find these two similar topics useful: and I am testing Tripp-Lite UPS unit compatibility with Struxureware software and found that Struxureware is not able to report any information, critical alarms from Tripp-Lite UPS unit in short or details email alert.
With respect.
(CID:153092328)
This answer was originally posted on DCIM Support by Paul O on 2019-12-20
Thank you for the information. I updated to the latest UPS MIB and nothing changed. I just downloaded the TrippLite DDF's yesterday so I assume they are the latest. We are in the process of upgrading the DCE. I guess I'll wait for that to be done and then see if anything changes. Thanks for your help.
(CID:153092348)
This comment was originally posted on DCIM Support by spezialist on 2019-12-20
From your question:
Mix of WEBCARDLX and websnmpcards and various Tripp-Lite models. WEBCARDLX version 15.5.2, websnmpcard version 12.06.0069.
I recommend using only the WEBCARDLX DDF-file and the DDF-file for your UPS (in total, there should be only two DDF-files for Tripp-Lite in DCE software).
With respect.
(CID:153092356)
This answer was originally posted on DCIM Support by Paul O on 2019-12-20
Sorry, I forgot to mention I did check those two articles you linked. The second one especially because that person is getting much more out of Alarm Configuration than I am, but, it could be because his version of DCE is newer.
(CID:153092354)
This comment was originally posted on DCIM Support by spezialist on 2019-12-20
Ok, let us know the result of your upgrade, please.
(CID:153092358)
This answer was originally posted on DCIM Support by Paul O on 2019-12-20
Correction, updated the UPS MIB did make a difference. I restarted DCE and waited a bit and now I see many more alarm options. I'll test them later today and see if it works and report back.
(CID:153092359)
This comment was originally posted on DCIM Support by spezialist on 2019-12-20
So it should be with the latest version of UPS MIB - this is important.
But it was possible not to restart the DCE-server, but simply to rediscover your UPS device in DCE-client.
With respect.
(CID:153092364)
This answer was originally posted on DCIM Support by Paul O on 2019-12-20
Hello. For reference if anyone else finds this. Updating to UPS MIB v.11 seems to have fixed my issue, thank you very much for your assistance.
(CID:153092372)
This comment was originally posted on DCIM Support by spezialist on 2019-12-20
Ok, very thanks for the good feedback 😀.
(CID:153092382)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.