Hi all
I have been getting this recommendation from DCO 7.5.0 when a device with 6 power inlets is connected to phases L1, L2 & L3 on both AP8886 rPDU's or AP7557 rPDU's in the rack. I have noticed that the devices, typically HP C7000 blade chassis, are connected this way in the belief of balancing the load over each phase.
Q1. Is this a correct approach to balance phase load at the device level ?
Q2. If not then what is the reason for the recommendation ?
Q3. Would best practice be to connect the same phase on both rPDU's for the 6 power inlets ? (i.e. 6 x L1)
Thanks in advance
Jim Davis - NIE Melbourne.
(CID:105470914)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:58 AM . Last Modified: 1 week ago
Hi Jim
Normally the recommendation we give is to connect load on just one phase. I understand that there can be circumstances where you have to do something else.
There are a couple of reasons for this the advice to put load on a single phase:
If you can balance the load by putting one chassis on L1 and one on L2 and a third on L3 and so, I would recommend that instead.
I hope that helps.
Best,
Niels
(CID:105470925)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:58 AM . Last Modified: 2023-10-31 11:39 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.