Hi team
have in my DCO sensors that monitor in each rack the cold corridor temperature and hot corridor that are integrated through the Rack_PDU
How can I use these real values in simulating the impact of air conditioners?
Norberto Castillo
(CID:126160556)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:14 AM
This comment was originally posted on DCIM Support by Ditte Drewer Mathiasen on 2017-10-09
Hi Norberto Castillo, thanks for posting. Let's hope you find your answer here.
kind regards Ditte
(CID:126160864)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:14 AM
This answer was originally posted on DCIM Support by Jef Faridi on 2017-10-09
Hi Norberto,
Simulated impact of cooling failure is based on calculated inlet temperature for individual racks compared to the maximum target inlet temperature for the room. The 2D cooling calculations do not use the measured temperatures. It models the airflow in the data-center and then uses these to estimate the temperatures. However, to improve the cooling calculations it is possible to specify some measured temperatures. These have to be specified manually - the values you can specify manually are: heater/rack known inlet temperature, cooler (cooling unit) known supply and return temperature.
Hope this helps,
Kind regards
(CID:126160946)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:14 AM . Last Modified: 2023-10-22 04:06 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.