Hi All,
One of our customer was using Demo DCO Colo licenses.
I decided to user DCO Base Linceses.
We removed DCO Colo licenses from the system and add DCO BASE licenses.
After that, Tags are dissappeared from the system.
Is there any method getting them back ?
Regards
(CID:105462355)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:08 PM . Last Modified: 2 weeks ago
There should be a backup of the solution on the server from before you removed the license. As a first step try to secure the latest backup from before the tags disappeared.
I haven't heard of this issue before, so I don't know if there is a quick way to get the tags back without restoring an older backup.
Which version of DCO is the customer using?
(CID:105462357)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:09 PM . Last Modified: 2 weeks ago
Hi Emre,
That make sense, because additional to the basic Operations license, Tags (and configuring tags) would require Capacity license. I don't think your Tags are disappeared from the system, but you need to install the required license, ie. the Capacity license.
Kind regards
(CID:105462431)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:09 PM . Last Modified: 2023-10-31 11:38 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.