Stulz WIB 8000 delay

I had added WIB 8000 SNMP to DCE using Stulz WIB version 23 but data collected very delay (above 4h and more)

 

Because sensors data was delayed so that alarm cannot correct.

 

I also configurated Stulz Units sync time with WIB 8000 hourly but this issue still happen

 

How can i monitor WIB 8000 or Stulz C7000 in DCE?

Tags (1)
6 REPLIES 6
Highlighted
Crewman

Re: Stulz WIB 8000 delay

Attached picture history report at 13:38 but WIB8000 lastes data at 9:23

Tags (1)
Highlighted
Ensign

Re: Stulz WIB 8000 delay

Hi, 

 

Just wondering if any lost communication capture during the "inactive" time of the data logging? How many devices you are monitoring with the DCE? What version of the DCE that is currently running? 

 

BR, 

 

TJ

Tags (1)
Highlighted
Crewman

Re: Stulz WIB 8000 delay

Hi

 

I'm using DCE 7.4.1 and monitor 78 devices with many modbus gateway

Tags (1)
Highlighted
Ensign

Re: Stulz WIB 8000 delay

Hi, 

 

It's recommended to upgrade from 7.4.1 to latest version 7.8.0. Version 7.4.1 has been removed from the official upgrade path due to some issues found with the version. However, you still can upgrade to 7.4.3 and follow the update path as shown in the link below: 

https://dcimsupport.ecostruxureit.com/hc/en-us/articles/360006668237-DCE-update-path

 

For alarm capture, another way is to increase the scan time for non-critical devices and decrease to scan time for the critical devices to capture important alarms. If alarms are not captured for the mentioned device (while the alarm is active), you might need to raise a request to DDF team (https://ddf.ecostruxureit.com/) to check the DDF used. Please prepare the necessary info before you approach them. To gather information, please refer the below link: 

 

https://dcimsupport.ecostruxureit.com/hc/en-us/articles/360006388878-How-to-create-a-device-walk-fil...

 

BR, 

 

TJ

 

Tags (1)
Highlighted
Crewman

Re: Stulz WIB 8000 delay

Hi

 

Can my version be upgraded directly to version 7.8 or must I go through the middle? Dose data and license remain the same?

Tags (1)
Highlighted
Ensign

Re: Stulz WIB 8000 delay

Hi, 

 

Yes, you can upgrade from 7.4.1 to 7.8.0, you must go through the version by version following the path. Please follow the upgrade path in the link below: 

 

https://dcimsupport.ecostruxureit.com/hc/en-us/articles/360006668237-DCE-update-path

 

You will need a valid software support contract that covers all your purchased license node in DCE in order for you to entitle to receive the upgrade files from the support. Do ensure to perform a full backup before the upgrade. 

 

BR, 

 

TJ

 