EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:13 AM . Last Modified: 2 weeks ago
Hi,
Where can I download the VM appliance for Struxureware Data Center Expert 7.x ?
(CID:110005692)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:13 AM . Last Modified: 2 weeks ago
Hi GB,
You can go here and fill out the form and they will e-mail you the download link:
http://updates.apc.com/isxc/surveys/vm/7.4.0/survey.cfm
Steve
(CID:110005694)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:13 AM . Last Modified: 2 weeks ago
Hi GB,
Instructions for downloading and deploying the trial can be found within knowledge base FA299551.
Regards,
Cory
(CID:110005698)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:13 AM . Last Modified: 2023-10-22 04:02 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.